Pinched from elsewhere.
Make your own minds up.
BS1363-2:1995 requires for double socket outlets that both socket outlets have loads applied via test plugs, 1 test plug having a load of 14 amps whilst the other has a load of 6 amps, making a total load of 20 amps on the cable supplying the double socket outlet. The double socket outlet is then subjected to this loading for a minimum continuous period of 4 hours or longer until stability is reached with a maximum duration of 8 hours (stability being taken as less than 1 degC rise within 1 h). The test is passed if neither the terminals / terminations, nor the accessible external surface, increase in temperature by more than 52 degC.
All MK socket-outlets are manufactured to comply with BS1363 part 2: 1995 and are rated at 13A per unit. Double socket-outlets have been manufactured and tested to exceed this rating by margin that allows electrical safety and reduces the risk of heat and mechanical damage to components due to overloading. It should be noted that BS1363 part 2: 1995 does not allow double sockets to operate at twice the permissible maximum loading and it should be remembered that double socket-outlets are not manufactured to be able to withstand a 26A load for sustained periods of time.
Research by ourselves and third party organisations has shown that all MK double sockets can safely withstand a continuous load of 19.5A for an indefinite period. Increasing the load slightly will begin to cause heat and mechanical stresses on the components in a relatively short period. Testing showed that a load of 22.3A was sufficient to cause heat stress that would cause a browning of the faceplates and sufficient heat to cause insulation damage to cable cores. A load of 24A for 43 hours was sufficient to cause significant heat damage to the material in which the socket-outlet was situated and within 75 hours sufficient to cause significant damage that would lead to the very real potential of fire.
MK recommend that users of their sockets consult professional design Engineers when designing installations to avoid the possibility of heat and mechanical stress to components and installations caused by overloading of MK socket-outlets.