Hi,

I am rewiring a house (circa. 1900) and I wanted to double-check the cable runs relating to the kitchen sockets.

My understanding of reg. 522.6.6 is that the cables between the sockets / spurs can be run horizontally, however an electrician that I am working with has advised me that "the cables cannot be run horizontally for more than 600mm. Therefore the socket runs should be run within 150mm of the floor and horizontal runs made to each socket before returning to the floor and along the floor again etc". Is my understanding of the 17th edition regs correct or do they need to be installed as he stated?

Also, what height (to the bottom of the sockets) do you personally place sockets above a kitchen worktop - I am aware of reg 553.1.6, but I am intrigued as to what height other people place theirs?

Any help would be appreciated.

Skimpy-Wan
 
Last edited by a moderator:
Does he mean just lying the cables on the floor? What a pikey! Nothing wrong with going horizontally from socket to socket as long as the cables are in line of the sockets
 
Hi,

Notes on cables run within a wall can be found on page 32 of Electricians guide to the building regulations. In this there is no mention of a limit to the length of a run between accessory. I would ask him to recheck this, as I would disagree with his/her statement about 600mm limitation.
 
To clarify:

My understanding of the regs are that the cables should be run within 150mm of the corner of walls / ceilings and can then be run horizontally or vertically, however he has stated that the cables should be "run within 150mm of the corner of walls / floor, but the legs to the sockets should be run vertically up to the socket outlet and then back to the floor zone (basically creating a U-shape between each socket outlet).
 
Last edited by a moderator:
To clarify:

My understanding of the regs are that the cables should be run within 150mm of the corner of walls / ceilings / floors and can then be run horizontally or vertically, however he has stated that the cables should be "run within 150mm of the corner of walls / floor, but the legs to the sockets should be run vertically up to the socket outlet and then back to the floor zone (basically creating a U-shape between each socket outlet).
Within 150mm of Ceilings and corners but not floors
 
he's talking out of his arse. 150mm of walls and ceilings, but no way across floor. you're right. he's wrong. end of.
 
Nothing wrong with that. But you can still run cables horizontally from one outlet to another. This is perfectly acceptable. Look at page 32 in Electricians guide to building regs.
 
Nothing wrong with that. But you can still run cables horizontally from one outlet to another. This is perfectly acceptable. Look at page 32 in Electricians guide to building regs.

Thanks Ken77, but unfortunately I don't have a copy of "Electricians guide to building regs" (maybe I'll order one late) as I tend to use the On-Site Guide and full BS 7671 text book.
 
Also, what height (to the bottom of the sockets) do you personally place sockets above a kitchen worktop - I am aware of reg 553.1.6, but I am intrigued as to what height other people place theirs?
 
Nothing wrong with that. But you can still run cables horizontally from one outlet to another. This is perfectly acceptable. Look at page 32 in Electricians guide to building regs.
Are you saying its acceptable to run cables within 150mm of the floor?
 
There's diagrams of safe zones all over mate, show him one of them. As said above, you're right he's wrong.
 
sockets above worktop need to be high enough above w/t so as not to damage flexes. so 4-6" to bottom of socket.
 
Centred between the worktop and wall-cabinets looks most aesthetically pleasing, and will satisfy the flex clearance as above. :)
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread Information

Title
Kitchen socket installation
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
37

Advert

Thread statistics

Created
Skimpy Wan,
Last reply from
telectrix,
Replies
37
Views
11,128

Advert

Back
Top