......Set at 500ma. Now this supplies several dist boards serving quite a few circuits. My question is do I install individual rcds set at 30ma at every board or to reduce incovenience when a circuit trips do I put all circuits on rcbo's( think of the expense of over 100 circuits). A lot of these circuits will supply fridges\freezers so might be a lot of nusieance tripping.Also cables running down stud walls serving light switches. 30ma? Sounds like its going to be an expensive excirise.
 
Going by a past experience I wouldn't hold your breath.

Same thing happened to me and no matter what I did or who I shouted at down the phone, I still had to make the install a TT, the whole street infact - 47 houses.
 
Hoover as this is a commercial enterprise you maybe able to evoke regulation 522.6.7 concerning cables buried in walls and 30mA RCD protection.

If you can prove that 500mA RCD will activate in 1sec for a distribution circuit and 0.2 seconds for a final circuit, then you could leave as is.

It is not ideal having such a large shop on a single up front RCD, but in these economic times often you have to make do with the hand your dealt with. I would be looking to make sure that 500mA RCD is operational and you may indeed need to change it for a new one to ensure safe operation.
 
Spin,


Quote from post#10 ...
You will also have to ensure discrimination between the RCDs.
If earth leakage is a problem, then you may have to provide individual RCD protection and a separate earth electrode to each DB, with the exposed-conductive-parts related to the DBs connected to the relevant earth electrode, double insulation would have to be provided for the part of the installation, between the origin and where the RCDs are situated... Quote...

Why would you need a separate earth electrode to each DB??
 
So that accumulated earth leakage doesn't cause an RCD to trip.

I would say, that if he were to provide multiple deep driven earth electrode positions, it would be better that he connected these positions together. It would/could provide a very decent earth path. It may also be very difficult to isolate building/service conductive parts, from one DB to others...

As this is a large store, it maybe that the surrounding ground to the property is tarmac or concreted over (car parking facilities) Which isn't particually good news when having to provide an earth electrode system, let alone in maintaining it....

Then there is the RCD device protection within this store, that needs sorting out!!! lol!!
 
Yes using a number of electrodes would/could provide a very decent earth path.
However the OP has already indicated that earth leakage is likely to be a problem.
It mayt be that the only solution is to divide the installation into parts, giving each part it's own RCD and electrode.
The earth leakage in one part of the installation would then be kept separate from the earth leakage in other parts.
 
Yes using a number of electrodes would/could provide a very decent earth path.
However the OP has already indicated that earth leakage is likely to be a problem.
It mayt be that the only solution is to divide the installation into parts, giving each part it's own RCD and electrode.
The earth leakage in one part of the installation would then be kept separate from the earth leakage in other parts
.

Very easy to say, but can be extremely difficult and often costly to achieve!!

First things first, ...the OP needs to start measuring any leakage problem areas. At least then, he will know the extent of any perceivable problems, and be able to to provide alternative suitable solutions.
 

Reply to large shop with an rcd at the origin in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
807
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
853

Similar threads

You would have thought they'd have a switch to flick on and off to engage an override. Not on each PIR but an actual light switch
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top