got a call on Saturday to say the newish washing machine is blowing the trip. when i had nosey around swapping leads and whatever i tried still tripping when starts a cycle.

its a tt installation with a ze of 14 ohms , insulation resistance of machine was as follows
l-e 1.3 M/ohms
n-e 12 M/ohms

earth continuity from plug to metal part of machine was 1.6 ohms

what i thought was an rcd is actual a voltage measuring device, apparently were installed before rcd came about , had no rating on it but has a yellow test button.

what else can i try or if i ring an appliance engineer what will he tell me. or what will he do.

thanks if your full of knowhow. im all ear or eyes
 
only get as far as page 3 all time..

.. need to clamp meter to measure earth leakage then can change device accordingly ..with a ze of 14 ohm i can get away 100mA - 500mA

would these devices be more sensitive than rcds?? id say no. but can somone explain how they work
 
you should be installing a 30mA RCD anyway. but, yes, by all means check installation leakage or global IR test before fitting RCD or you might end up spending an extra day sorting out problems which you haven't allowed for in your quote.
 
only get as far as page 3 all time..

.. need to clamp meter to measure earth leakage then can change device accordingly ..with a ze of 14 ohm i can get away 100mA - 500mA

would these devices be more sensitive than rcds?? id say no. but can somone explain how they work

Well if there is a Voltage trip chances the fuseboard isn't 17th compliant?
If I were you I would be giving the customer two choices - direct replacement with 30ma rcd (not recommended)
Fuse board upgrade.
then fix any problems like washing machines.

Voltage trips operate when the touch voltage rises above 50V (unless I'm mistaken)
but are unreliable due to parallel paths making them inoperative.
 
I havent measured the earth leakage yet.

If i know how these voltage devices operate then i can start from the start of working out what is going on.. Dont forget im a newbie so never seen one of the devices before or worked with them
 
irrelevant how or if they work-- it wants ripping out . end of. i wouldn't expect my motor mechanic to know how steam engines worked ( that's one for engineer54, he'll know. LOL.)
 

Reply to leakage in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
285
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
786
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
804

Similar threads

  • Question
Just an update for anyone interested, I got another rod in outside today, which has lowered the Zs db to a more healthy 53ohms. The oven elements...
2
Replies
19
Views
3K
I opened up the CU again and the round junction box above and what I found was the blue and brown wires coming in from the wall just above the 15a...
2 3
Replies
33
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top