i=p/u

-
Arms
Joined
Dec 9, 2010
Messages
7,520
Reaction score
816
Location
Northern Ireland
got a call on Saturday to say the newish washing machine is blowing the trip. when i had nosey around swapping leads and whatever i tried still tripping when starts a cycle.

its a tt installation with a ze of 14 ohms , insulation resistance of machine was as follows
l-e 1.3 M/ohms
n-e 12 M/ohms

earth continuity from plug to metal part of machine was 1.6 ohms

what i thought was an rcd is actual a voltage measuring device, apparently were installed before rcd came about , had no rating on it but has a yellow test button.

what else can i try or if i ring an appliance engineer what will he tell me. or what will he do.

thanks if your full of knowhow. im all ear or eyes
 
got a call on Saturday to say the newish washing machine is blowing the trip. when i had nosey around swapping leads and whatever i tried still tripping when starts a cycle.

its a tt installation with a ze of 14 ohms , insulation resistance of machine was as follows
l-e 1.3 M/ohms
n-e 12 M/ohms

earth continuity from plug to metal part of machine was 1.6 ohms

what i thought was an rcd is actual a voltage measuring device, apparently were installed before rcd came about , had no rating on it but has a yellow test button.

what else can i try or if i ring an appliance engineer what will he tell me. or what will he do.

thanks if your full of knowhow. im all ear or eyes
If you have a new (ish) washing machine that is tripping a VOELCB then I would start by saying the machine is faulty and should be returned to the manufacturer if it is under warranty.
You would certainly recommend to the customer the replacement of the VOELCB with a suitable system but they do not have to take your advice.
If you are just operating as a washing machine repair man then the installation is not your responsibility, but is something that should be highlighted with the customer.

You could try testing continuity to earth (not IR) for the washing machine and then operating the cycle start switches and see what turns up.
If it is not totally digital then you may immediately get a fault.
The first thing a washing machine does is power up the level sensor and start adding water, so this could be your first port of call: water supply solenoid or damaged water level sensor. After that call an appliance engineer!
 
Only need 30mA on circuits for additional protection, i.e buried in walls less than 50mm deep, rooms with bath/shower and all circuits with sockets
All other circuits on a TT require maximum 100mA RCD protection

As there is usually no chance of the normal ADS being effective on a TT system, RCD is unfortunately the prime protection. 100Ma is the older max rating, so as Tel stated, All circuits on this TT installation need 30mA RCD protection...

Having 30mA RCD protection on the circuits in the form of dual RCD or RCBO's .....Then a 100mA S type up front RCD would be classed as ''Additional Protection''!!...lol!!
 
Put it this way it all depends on the reputation you want to get,fit a 30mA rcd and its right rit a 100mA rcd and someone may come along in the future and say "which cowboy fitted this? should have been 30mA " the customer will probably take their word and you look a pratt as well as getting a bad name.My course of action would be advise cust to get engineer to deal with machine as its clearly faulty and also advise cust on getting rcd soted.That way you come out looking like a decent sparks.
 
well guys depending on the ra value will determin what rating the upfront rcd can be, 30mA to 500mA, this is cause disconnection times cant be met. correct me if im wrong. so its all about the Ra.

as for exisiting installation not rcd protected , i believe i am not required to update circuits to be covered with 30mA rcd.

the easiest way todo this would put 30mA rcd on the tails but the question then is , will it hold the whole farm house

- - - Updated - - -

but thanks for your inputssssss
 
Try a plug in RCD or temp board with an RCD. If the RCD operates before the VOELCB then there is definatly a fault on the machine.
It's hard to IR test new appliances to diagnose a fault as they are all electronically controlled so the faulty part probably won't be switched in if tested dead. Does the brown box trip immediatly the machine is turned on or after a few mins? If straight away it is unlikely to be the usual culprits. (element, motor, pump etc)
If the VOELCB blows before the RCD you are back to square one, sorry.
The earth continuity may well be higher than 0.1 ohms in reality, it depends on the length of the flex and the part of the machine the reading was taken from.
Definatly recommend upgrade to 17th edition board, upfront 100mA or 30mA RCD may give you a world of trouble. Good luck in getting the customer to go for it though. (cor blimey, what a rip off mechant, I only asked him to fix the washing machine and he want me to spend ÂŁ300 on a new fuse box) I blame too many cowboy builder programs.........
 
cheers tonkatoy , yh you got it one, i only wanted the washing machine fixed.

and yeah the voltage device trips as soon as you start a programme so the water level device as someone said this is the first part that operates.... maybe maybe maybe dunno.
 

Reply to leakage in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
285
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
786
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
804

Similar threads

  • Question
Just an update for anyone interested, I got another rod in outside today, which has lowered the Zs db to a more healthy 53ohms. The oven elements...
2
Replies
19
Views
3K
I opened up the CU again and the round junction box above and what I found was the blue and brown wires coming in from the wall just above the 15a...
2 3
Replies
33
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top