led and photocell. | on ElectriciansForums

Discuss led and photocell. in the UK Electrical Forum area at ElectriciansForums.net

S

simon07904

recentlly fitted 4x23w,1x50w flood,and 2x80w floods via a photocell outside. the photocell keeps failing after about 4 weeks and ive changed it twice already. does anyone know why as im confused. the cell is capable of switching 1000w so is easily suitable(so i thought).. thanks simon
 
Have you checked the start up current of your fittings as LED's can have start ups hundreds of times greater than their running currents. I would imagine you are overloading the photocell.
 

Reply to led and photocell. in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
702
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top