Guest154

hi having some problems with led floodlight , firstly had 17 140w led floodlights on one circuit wired with a 10mm single line swa , started with 16 amp mcb and it kept tripping on start up not every time , tested all the cabling and and put the clamp meter on it cuming up with just over 10 amps on start up , so i changed the mcb to a 20 amp still tripping then a 32 still tripping finally a 40 amp mcb and it has stopped tripping , i then used the same floodlights on another 2 jobs 1 with 4 on a circuit and the other with 12 on a circuit and the same thing happened had to keep uppin the mcb , they are not cheap fittings ÂŁ400 a piece , i did contact the company that make them but the say they have had no issues like this b4 , anyone have any ideas
 
what was it sayin about start up current murdoch

That some LED lights have extremely high start up currents.

Edit:

Lamp ............................................ Peak Inrush Current ... Steady Current ... Real Power ... Apparent Power ... Power Factor

50W GU10 Halogen ..................... 2200mA ...................... 222mA ................ 53.4W ........... 53.4W ..................... 1.0
LEDlite 4.9W GU10 LED ................ 416mA ...................... 355mA .................. 5.9W ........... 53W ........................ 0.11
Halolite 1.5W GU10 LED (old) ...... 2100mA ........................ 23.4mA .............. 1.04W ........... 5.7W ...................... 0.18
LEDLite 10.5W LED downlight ........ 420mA ........................ 54.6mA ............ 11.6W ........... 13.2W ...................... 0.87


apologies to the chap who did this but I'm sure he won't mind me plagerising it!
 
clamp meter is only showing just over 10 amps on start up

Is this with a peak hold function or are you just catching the max reading visually?

(The investigations into LED start up currents and power factors were mine on another board.)

Somewhat related, I ended up putting three LED drivers for under-cupboard LED strip lights onto a 6A type C MCB as the inrush was sometimes measuring 50A for each driver on startup.
 
hi andy , contacted the company that sell them again but they say they have had no issues like this with these lights , not sure if i believe them but they are holding for now , i can only assume that these guys are right about the start up current being so high , next time i am on the sites i will try the clamp meter on them again using the peak hold function see what it comes up with , cheers
 

Reply to led floodlight problems in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
My bafflement increases. I swapped the offending light with one elsewhere on the back of the house - one of those that's on a circuit of its own...
Replies
5
Views
1K
  • Question
Its important to remember that a plug top fuse is just a rewireable fuse that's convenient to change and shouldn't be confused with a HRC fuse...
2
Replies
15
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top