If it is capable of providing 20A then every part of the circuit after that point needs to be able to deal with carrying 20A without overheating.
Exactly, as in any other circuit design. You need to make sure the circuit (to the end of the strip) has a low enough impedance to activate the protective device (be that fuse or overload protection in the psu) before the strip catches fire.