Guest viewing limit reached
  • You have reached the maximum number of guest views allowed
  • Please register below to remove this limitation
Happy new year guys,

I installed a new Lewden CU today and all the type A RCBOs failed when tested at x5 (150mA) at the end of the circuit. However, when tested at the terminals of the RCBO they tripped in around 38/39ms. I am aware that Hager have had issues with their 61008 RCCBs and suggest testing them with 250mA test current, are they any know issues with Lewden switchgear?

Thanks
 
Never had a problem with Lewden kit but I always find it easiest to test at the device with the cables removed.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

Joined
Location
uk
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Other

Thread Information

Title
Lewden 30mA type A RCBOs
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
1
Unsolved
--

Advert

Thread statistics

Created
andrew8902,
Last reply from
Strima,
Replies
1
Views
1,731

Advert

Back
Top