Wired a house a while back and just getting around to putting up the main light in the hall last week, (20kg hanging pendant ), there is 3 switch linens on the circuit, outside lights, 6 spots in the hall then the pendant, before installing this light all over lights were working fine and all switching was fine but after installing it the MCB is tripping, the main hanging pendant will turn on but as soon as you turn the light off the MCB trips, cannot understand why light is staying on but then suddenly trips when the switch is turned OFF any ideas or anyone had a problem similar, really don’t fancy taking this light down as it was a serious hassle to put up in first place in an open hallway, the light is two way wit an intermediate switch but all seems fine at the switches, I disconnected the light from the roofspace JB and connected in a lamp drop to make sure all was working and the lamp drop is turning on and of as required from all switches with no MCB tripping
 
Wired a house a while back and just getting around to putting up the main light in the hall last week, (20kg hanging pendant ), there is 3 switch linens on the circuit, outside lights, 6 spots in the hall then the pendant, before installing this light all over lights were working fine and all switching was fine but after installing it the MCB is tripping, the main hanging pendant will turn on but as soon as you turn the light off the MCB trips, cannot understand why light is staying on but then suddenly trips when the switch is turned OFF any ideas or anyone had a problem similar, really don’t fancy taking this light down as it was a serious hassle to put up in first place in an open hallway, the light is two way wit an intermediate switch but all seems fine at the switches, I disconnected the light from the roofspace JB and connected in a lamp drop to make sure all was working and the lamp drop is turning on and of as required from all switches with no MCB tripping
Looks like that light you don't want to take down will need looking at, as others have said have you done any testing?
 
#6 was my first thought, so IR test the switching cabling to E and N with the switches in all positions.
If you have access to the junction box in the roof space for the pendant then test for IR on the connections to the light fitting just in case #3 is correct.
The highest current will be drawn when the arc is sustaining across the opening light switch so if the problem is relating to a specific one of the three switches then try temporarily wiring that pendant switch to new switch and see if the problem recurs. Perhaps even just wiring it to a one way switch (if you have wired it in 3 wire wiring) from the supplied switch and see if the problem is related to the three way wiring.
 
20kg ....one heavy pendant is that!
How many lights and what type and voltage are involved/
transformer?...led, or what?
What size and type of breaker? Some recommend C type.
 
If the light is on a 1G 2 way switch, check that the terminal screw from the unused way isn't sitting on/touching the lug/back box.

I had that problem on an outside light years ago. Worked ok when on, but tripped as soon as they turned it off. As soon as I pulled the switch plate forward, the little terminal screw fell out and I could see where it had been touching/arcing on the bottom lug of the back box.

Jay
 
Could be a transient spike from the collapsing magnetic field in the transformer when you turn it off suddenly with a switch. Much like a switch start fluorescent. In theory, the breaking switch contact should prevent any extra current from this spike reaching and tripping the breaker, but breaking a contact isn't instantaneous and as @Richard Burns has mentioned there's the possibility of an arc being sustained across an opening light switch.

As per @ipf 's post - what size and type of breaker? If Zs and other factors will allow it, perhaps go to a type C (if not already)? Failing that, perhaps some sort of surge protective device (stubber?) located near the big light?
 
Could be a transient spike from the collapsing magnetic field in the transformer when you turn it off suddenly with a switch......
@Richard Burns has mentioned there's the possibility of an arc being sustained across an opening light switch.

As per @ipf 's post - what size and type of breaker? If Zs and other factors will allow it, perhaps go to a type C (if not already)? Failing that, perhaps some sort of surge protective device (stubber?) located near the big light?

Switch already damaged ,Snubber required.
(has MCB been ruled out for being over sensitive )
 
Yea light has quite a large transformer inside with approx 14 lamps dropping, really hoping it wasnt a faulty light but can’t think of any other reason why it would be tripping
Give some details...breaker and fitting, as previously said. Did you read the instructions fully?
Everybody is surmising.
 

Reply to Light tripping!! Any advice in the Commercial Electrical Advice area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
197
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
248
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
346

Similar threads

My guess is an earth to N fault in the damaged light fitting. This will become a problem when other devices draw large currents.
Replies
2
Views
317
Have you notified Building Control of these works?
2
Replies
19
Views
910

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top