if u installed the circuit then u know u have correct polarity, unless ur a dumb nut
Mistakes are made sometimes.
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss lighting circuits on PIR's in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
if u installed the circuit then u know u have correct polarity, unless ur a dumb nut
I know what you're saying but for polarity you are supposed to confirm that single-pole devices etc. are connected in the line conductor only. Therefore you need to operate the switches etc. and also the centre pin of bayonet cap lampholders.
if u installed the circuit then u know u have correct polarity, unless ur a dumb nut
The R1R2 test is not there to proove polarity only to proove the earth is present and at a reasonably suitable value, hence having the option of doing an R2 test only.
It's a plug in ceiling rose, most are made by Klik so they are generally referred to as this.