The R1R2 test is not there to proove polarity only to proove the earth is present and at a reasonably suitable value, hence having the option of doing an R2 test only. There is always the choice of R2 only test but this does involve a rather long earth lead which can be difficult in some situations and this is why the R1R2 was developed as a means to make the testing more practical. Surely with this in mind the RnR2 will do just as well for a test in this situation, particularly if speed is an issue. I would not use the R1R2 test to proove polarity as such, it may just end up being a way of prooving it in the end, but there are better ways of prooving polarity than that.;)
 
The R1R2 test is not there to proove polarity only to proove the earth is present and at a reasonably suitable value, hence having the option of doing an R2 test only.

You could take an R2 reading of course, but it means that you will then need to prove polarity separately. So connect your wander lead to the line conductor and operate switches and single pole devices, check centre-pins of Edison Screw lampholders etc.

Probably would have saved time by killing two birds with one stone by using continuity test method 1.
 
Hi Pennywise and M25 Maintenance,

Is that the Ashley Klik system with a plug connector with angled pins? I have seen it and it seems a good idea, useful for time saving later on etc, though havent used it.

Is it any good and what do would you say the best or worse bits with it are?

Thanks,

Rex
 
Klik got bought out by Hager like Ashely did. Greg rose is another term as you say, take your pick ;) . They are great if your just looping in and out with the neutral and switchline, they can be a nightmare if you try 3 plating them but thats usually just the first one if it hasn't been fed straight from the switch bank.
 
Last edited by a moderator:
The down side of them is the *****ing cost, especially the prewired. I cant see that they should be any more than a double socket in construction but are over twice the cost......... thieving ***** :D
 
Last edited by a moderator:
Hi Stretchyboy,

Yes I agree when you compare the prices of stuff it does raise the question of 'why the rip off?' I suppose it is down to the usual supply and demand thing. The more competition the lower the price (or should be at least) or the greater the build numbers.

Hopefully the prices will be reasonable (in the customers eyes).

Best wishes

Rex
 
4 pin click/greg/whatever, with the two lives in a choccy block/wago.
Anything else is a bit of a waste of time (unless you cant get to the greg of course).
Either that, or stick both live's in the same terminal in the PIR.
 
Last edited by a moderator:

Reply to lighting circuits on PIR's in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
808
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
857

Similar threads

You would have thought they'd have a switch to flick on and off to engage an override. Not on each PIR but an actual light switch
Replies
5
Views
1K
The existing wiring shows both brown wires into the same terminal. One should be in the terminal it is in now and the other in the terminal next...
Replies
1
Views
225

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top