Spudnik

Evening chaps,

Did a PIR other day, and the lighting has been wired as a ring and not 2 radials.

Now, i could hunt around and try and split it, but i was wondering what your thoughts were on this.

Its been like it for a fair few years on a 6A MCB and the owner has never had a problem with overload.

In other words... mark it on report as satisfactory and note it on the deviations or not?

Ta muchly.
 
Nothing wrong with lighting on a ring,external lighting being a good example
It seems the only thing to pick up on is the nuisance element of all being on that one circuit
I would call it satisfactory but also, I would code 4 it for that, and note the circuit design on the comments
 
No real issue there mate....best to note it on the cert though. As the OCPD for the circuit is not higher than the CCC of the cable (unlike a coventional ring final) then no real worries of overloading it at one point should someone come along at a later date and ad to or extend etc.
 
cheers matey, im still a little wet behind the ears at only 23.

Good job us youngsters have got access to experienced people on here who dont turn up their nose and moan about inexperience!
 

Reply to Lighting RFC!?!? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
244
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
717
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
686

Similar threads

I was at the other end of the results spectrum today. As I was driving home I had a call from my "Mrs Richards from Fawlty Towers" lady, very deaf...
2
Replies
20
Views
1K
There is one reason to have an inspection every three years instead of the five. Itā€™s more work and money for them šŸ˜šŸ˜
Replies
15
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top