So whats is your ideas...5 amp mcb with main switch 30ma rcd....nice house , dry etc ...put any combination of lights on and after around 4-5 minutes mcb blows.....the lambs are varied but i can not see any overload and it will do it with only a handful on...if you leave say 1 or 2 lights on it will not blow...and any selected but add load in any are even light it blows...so far my views is could be mcb fault but then why would it not blow with less lights...small fault...but why would that not take out rcd ?..and this has been doing it for years not short term...a mcb blowing seems overload but i can not see that as it does it well in on loading...any views ?
 
IR test the circuit both LN-E and L-N (with lamps removed).An RCD will trip on a low IR to earth,it will not trip on a L-N fault,that would trip the OCPD.Eliminate that first. If IR is satisfactory clamp the line and see what the circuit is pulling.
My guess would be a 'tired' mcb. But test for faults first.
 
yeah going for the mcb first .. if not i will be taking lamps out and testing as described or some disconnections...certainly its not overload....is there anything else on the thermal overload i am missing? there is extensive dimmers...some of the non fire rated downlights ..but not many...if a dimmer was erratic would it cause this rather than show a dimmer breaking down...gut feelings.
 
Have you clamped the load ... unless you wired them yourself don't assume that no other loads are tapped into the circuit.
Have you done any testing and if so what results?

Also check post 3 as a possiblity.
 
Last edited:
no tests at the moment as i am just throwing it out to see views...the clamping the load i understand but its does it with very little load but an increased load...i mean 5 amp mcb blowing with say 500ws on but held at 400ws...also turn the light off in lounge and put dining room on does the same yet load could be 500 or less...keep on light or two on say 300w any variation holds fine...so i am thinking along your routes and will go that path.....no other items other than the lights are affected when it blows so i assume no sockets took off it......etc...good one isnt it and i have 35 years...i like these ...i admit the con unit is older but apart from rcd control i could not tell them its HAS to be renewed ...
 
Well what's the point in not testing, it could be a number of things, all that everyone's doing is guessing! Get some tests done and take it from there. If it was me I'd clamp it first to rule out excessive load then carry out further tests if needed. It could even be an earth fault and the rcd is stuffed! Without testing you'll never know. I would have thought with 35 years experience you'd know that.
 
With 35 years i do know that...was a simple chuck it out there to see what as "electricians" your views were...not guessing as such just time served hunches...of course i will be going down all the routes but i thought i would ask to see if anyone came up with a thought i had not considered. i have not done any tests yet as i have not started although i have been to see the problem ...most of us know the routes but surely you have come across the sparky that says "i had that once ..guess what it was " or would you say i can not guess unless you tell me you tested... i only seeked to see views on hunches not be treat like a schoolboy
 
Last edited by a moderator:
You have been given some very helpful advice and I can not see why you have such an attitude towards other members replies? You have only just stated that you have not had the chance to carry out tests, only looked at the job. If you told us this in the first post things would have been a lot clearer.
 
Last edited:
With 35 years i do know that...was a simple chuck it out there to see what as "electricians" your views were...not guessing as such just time served hunches...of course i will be going down all the routes but i thought i would ask to see if anyone came up with a thought i had not considered. i have not done any tests yet as i have not started although i have been to see the problem ...most of us know the routes but surely you have come across the sparky that says "i had that once ..guess what it was " or would you say i can not guess unless you tell me you tested... i only seeked to see views on hunches not be treat like a schoolboy

Although the mod has already edited your response may I offer advice, your profile about your electrical experience hasn't been filled nor did you present this in your opening post thus we don't know if your still wet under the collar with minimal experience or as you have now revealed you have 35yrs under the belt, this puts us in a difficult position of guessing how to respond ... to a newby all above advice is relished but to someone with 35yrs experience you may feel your been condescended hence your response but until we are told we have to guess and usually this is done by the nature of the question.

Asked the same question on site then I would talk totally different to a seasoned sparks like yourself than a newby on his first year qualified.
 
Last edited:
With 35 years i do know that...was a simple chuck it out there to see what as "electricians" your views were...not guessing as such just time served hunches...of course i will be going down all the routes but i thought i would ask to see if anyone came up with a thought i had not considered. i have not done any tests yet as i have not started although i have been to see the problem ...most of us know the routes but surely you have come across the sparky that says "i had that once ..guess what it was " or would you say i can not guess unless you tell me you tested... i only seeked to see views on hunches not be treat like a schoolboy

I'm guessing that the 'condescending' line that was removed was aimed at me,if so, am I bothered....no, skins far too thick and besides I grew a pair a long time ago! What I will say is that it sounds like an interesting fault which most on here including myself would relish the task of sorting, and if found to be rather odd or unique would then start a thread sharing the information gained. I know 1 or 2 on here who would even drip feed information and set it out as a 'see who's first to guess what the fault was' quiz.
You could gain a lot of respect by coming back on here and reporting your findings, that I can guarantee will be well received.
 
Last edited:
I'm guessing that the 'condescending' line that was removed was aimed at me,if so, am I bothered....no, skins far too thick and besides I grew a pair a long time ago!

It was not aimed at any individual member so dont take any personal offence. It was a rant on a thread from a new-ish member that has been removed so not to inflame the thread. No big deal really, dont worry about it.
 
After 35 years, to be honest I’d be too ashamed to ask for random ideas when I couldn’t be bothered to do initial any testing.

In his defense he only looked at the job, so he only flicked on a few switches and saw the problem that the customer has told him. Says he is going to do the job and we can only assume that a time served spark will take test equipment with him.

The OP has been given some great advice but if this was me I would check the terminations in the CU, then the ceiling roses, then the switches, clamp test before and after the visual checks. After all of thesr trips, the mcb will be knackered so change it. Simple fault find and rectification in my mind.
 
Paul, there’s many ways to approach a job, asking on the net for wild ideas certainly wouldn’t be my approach.

Would you ask before doing some basic tests?
I’d do the tests and then think about them.
Yes, there has been some good advice, but they are guesses.

I worked with a guy, “the last time this happened it was xxxx”. He could add hours to a shutdown by diving off hither and yon.
The same guy confidently told me the main fuses to a drive were OK, they were sat on a steel bench, the bench tested at 0Ω across the fuse.

Our trade was founded on physics and logical thinking, what happened?
 
Last edited by a moderator:
my money's on a tired/stressed MCB, having had too many cheap lamps blow over a period of time, but , pending the OP doing some testing, it's a shot in the dark. ( pun intended ).
 

Reply to Lights blowing mcb in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
What is the distance from the point outside the house to the shed?
Replies
8
Views
646
  • Question
Its important to remember that a plug top fuse is just a rewireable fuse that's convenient to change and shouldn't be confused with a HRC fuse...
Replies
15
Views
1K
  • Question
And exciting when that Hager AFDD finally tripped 😂
2
Replies
28
Views
2K
nicebutdim
N
  • Question
Why not fit a self contained SPD fed directly from the Henley blocks, and free up a bay? Could probably make one up from whats there, using a...
2
Replies
47
Views
4K
  • Question
Top tip, though too late now, is always photograph what you are about ti disassemble. And again after reassembly. It helps if something...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks