if your replacing a like for like shower if its not rcd protected does this have to be done as well
 
guys

if your replacing a like for like shower if its not rcd protected does this have to be done as well

Long after the event i know, but only found your question on a search. Answer is from HERE


EDQ10
If I replace an existing electric shower, do I now have to provide RCD protection for it?

EDA10
No, unless RCD protection is required by the manufacturer’s installation instructions, or a new circuit is required (to provide for increased load, for example).​


134.1.1 510.2
 
According to their website / installation instructions, in Credas' website they don't mention RCD's but Tritions' do recommend the use use of a 30ma RCD.


Quote
-------

A 30mA residual current device (RCD) must
be installed in all UK electric and pumped
shower circuits. This may be part of the
consumer unit or a separate unit.
 
Last edited by a moderator:
Long after the event i know, but only found your question on a search. Answer is from HERE


EDQ10
If I replace an existing electric shower, do I now have to provide RCD protection for it?

EDA10
No, unless RCD protection is required by the manufacturer’s installation instructions, or a new circuit is required (to provide for increased load, for example).​


134.1.1 510.2

I have to admit even if the manufacturers did not advise fitting a RCD I think as it's a shower it is the few times I would go against the guidance of the Regs and fit one.

Know if you have the proper disconnection time on a fuse or MCB it would be safe ....................but do like that additional protection of 30mA and 0.04 secs
 
It must be a shower that has been on the shelf for a while, or an import. All the main stream showers that I have fitted for the last year or 3 have all stated must have a RCD, or that it must be installed in accordance with BS7671 wiring regulations in which case it must have a RCD anyway.

Cheers......Howard
 
Even if it is a like for like, it can go on a minor works cert but will still need notifing as it's a special location

Like for like replacements are not notifiable, even if carried out in a special locations, unless it is a consumer unit.
Have a read of the IEE's electrician's guide to the building regs,parts b and c on page 22.
 

Reply to like for like shower in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
288
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
790
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
813

Similar threads

M
  • Article
Tiling on Universal Shower Bases Hi there - I’m hoping to get some advice. I’m a builder, based in Melbourne, Australia. I’ve recently done a...
Replies
0
Views
136
Melbourne Builder
M
J
  • Article
Traymate Shower tray Hi guys, This is my first post so apologies if this isn't the right section for the post. I'm a qualified plumbing and...
Replies
0
Views
150
Jeefa
J

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top