if your replacing a like for like shower if its not rcd protected does this have to be done as well
if your replacing a like for like shower if its not rcd protected does this have to be done as well
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss like for like shower in the Australia area at ElectriciansForums.net
Well I've just been on with ELECSA, and they agree with me, if the MCB you are swapping supplies circuits within a special location then it bneeds to be notified. You are changing the safety characteristics of the circuits, all usual testing should be carried out on the circuit including the new RCD test for the RCBO, a minor works cert is sufficient, however it should still be notified.