So was testing a house today (new build)
When I came to testing on of the ring finals in the house, when testing insulation resistance the live and earth legs on the ring are clear but live to the earth on cpc’s on the cooker circuit, other ring, downstairs lights and heating its bang down I’m thinking something to do with damp walls? But every time Other circuit tested out fine on IR
 
What I meant was if for say the cooker circuit you did:
L to N and got >999mohms
N to E and got >999mohms
And L to E gave 0mohms

then you can be pretty sure there’s a dead short somewhere as
1) any dampness would not cause zero anyway
2) any dampness would be unlikely to affect just one core

So I would then use the (low resistance) continuity function to measure more accurately what the resistance is between L and E. That can then give you some idea where the fault is.

As there’s a rfc affected, if you take both ends out of CU and measure L to E on continuity at the sockets the resistance should drop as you get nearer the fault and the fault will be between the two lowest readings.

It interesting that so many circuits are apparently affected. Forgive the silly question but are you testing in the top of the breakers and are the breakers all off?
 
What I meant was if for say the cooker circuit you did:
L to N and got >999mohms
N to E and got >999mohms
And L to E gave 0mohms

then you can be pretty sure there’s a dead short somewhere as
1) any dampness would not cause zero anyway
2) any dampness would be unlikely to affect just one core

So I would then use the (low resistance) continuity function to measure more accurately what the resistance is between L and E. That can then give you some idea where the fault is.

As there’s a rfc affected, if you take both ends out of CU and measure L to E on continuity at the sockets the resistance should drop as you get nearer the fault and the fault will be between the two lowest readings.

It interesting that so many circuits are apparently affected. Forgive the silly question but are you testing in the top of the breakers and are the breakers all off?
For the cooker circuit all tests are clear including L-E the only one that’s down is L on the sockets the other cps I was disconnecting the cpcs one at a time from earth bar
For example
Clip on L from sockets circuit then clipping onto cpc for cooker that’s down
 
What I meant was if for say the cooker circuit you did:
L to N and got >999mohms
N to E and got >999mohms
And L to E gave 0mohms

then you can be pretty sure there’s a dead short somewhere as
1) any dampness would not cause zero anyway
2) any dampness would be unlikely to affect just one core

So I would then use the (low resistance) continuity function to measure more accurately what the resistance is between L and E. That can then give you some idea where the fault is.

As there’s a rfc affected, if you take both ends out of CU and measure L to E on continuity at the sockets the resistance should drop as you get nearer the fault and the fault will be between the two lowest readings.

It interesting that so many circuits are apparently affected. Forgive the silly question but are you testing in the top of the breakers and are the breakers all off?
All breakers off just in the top individually testing them to earth
 
Basically 0 M ohm

So was testing a house today (new build)
When I came to testing on of the ring finals in the house, when testing insulation resistance the live and earth legs on the ring are clear but live to the earth on cpc’s on the cooker circuit, other ring, downstairs lights and heating its bang down I’m thinking something to do with damp walls? But every time Other circuit tested out fine on IR
Are all the conductors under test dissed from the CU INCLUDING THE MAIN EARTH During testing?
 
For the cooker circuit all tests are clear including L-E the only one that’s down is L on the sockets the other cps I was disconnecting the cpcs one at a time from earth bar
For example
Clip on L from sockets circuit then clipping onto cpc for cooker that’s down
Normally you IR test with all CPC connected to the MET so a fault from, say, L to some wet brickwork will appear. Only then would you remove the CPC for that circuit to try and find out if the fault is L-CPC or L-Earth somewhere.

I see @Pete999 just posted about that!
 
Normally you IR test with all CPC connected to the MET so a fault from, say, L to some wet brickwork will appear. Only then would you remove the CPC for that circuit to try and find out if the fault is L-CPC or L-Earth somewhere.

I see @Pete999 just posted about that!
They was all connected to start with then I started disconnecting some then still testing via the MET to see which cpcs were bringing it down
 

Reply to Live earth fault?? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
361
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
920
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Very technical :D
    • Like
Replies
9
Views
385
I was at the other end of the results spectrum today. As I was driving home I had a call from my "Mrs Richards from Fawlty Towers" lady, very deaf...
2
Replies
20
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top