cliffed

-
Arms
Joined
Dec 20, 2009
Messages
2,185
Reaction score
698
Location
Worcester
what’s your take on working on live DB’S,connecting circuits & installing mcbs.
 
Even if isolated if you restored the power it still would have exploded yes?
Or was the issue the cover wasn’t reinstated before turning on the mcb?
(I’m not advocating live working by the way)

Actually, no, the problem was that busbar termination screw in the MCB which should have been captive wasn’t. As the guy tried to tighten it it went thru the open side of the MCB and touch the neighbouring phase connection which resulted in a direct short between two phases. If the power had been off it would not have happened.
 
It's worth remembering that there could be the potential for a substantial fault current which could pose serious risk to personnel working on it. It's actually quite a dangerous practise.
 
I must say I always work live

The biggest scare I got was when a general operator went to reach over my shoulder, he was mesmerised by the 400 amp copper bus bar.

He was looking to take it home for scrap, ready to ask me if I needed it.

:dizzy:
 
I must say I always work live

The biggest scare I got was when a general operator went to reach over my shoulder, he was mesmerised by the 400 amp copper bus bar.

He was looking to take it home for scrap, ready to ask me if I needed it.

:dizzy:

Never heard a John Thomas called a 400 amp bus bar before, every day is a school day on the EF website........ no wonder you where scared.......
 
The biggest scare I got was when a general operator went to reach over my shoulder, he was mesmerised by the 400 amp copper bus bar.

Don't... I did a job on Saturday adding a couple of socket outlets in a nice house in Newport. The lady of the house asked a question about the testing (insulation resistance at that stage) whilst I was at the open consumer unit.

"Ooh, look at that cobweb" she said as she reached into the consumer unit and swept it away with a finger, just above the live bus bar!
 

Reply to Live works,on DB to do or not to do in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
438
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Thanks, I was reasonably confident but nice to confirm. That was the original install getting power to the outbuilding, done by an electrician we...
Replies
8
Views
471
  • Question
One of those backlight Chinese testers may have helped that’s if the tester didn’t catch fire or electrocute you. LED TV Backlight Tester 12W LED...
2 3 4 5
Replies
68
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top