I have a 230 Volt single-phase circuit with a 100 Amp cutout fuse and a 100 Amp MCB switch, so the supply is rated at 23 kVA.
Only about 13% of my total energy consumption is electricity. The remaining 87% is natural gas, supplying the following appliances (kW figures are net output power):-
22 kW boiler, 3 kW fan-flued convector heater. 8 Kw cooker.
After (if?) natural gas is turned off some time in the 2030s I can have 3-phase installed (at vast cost) to give me total kVA 55.15 at 230 Volts. As you can see, this offer is tied to reducing the supply capacity per phase to 80 Amps. So a connection from one phase (and the neutral) to my existing single-phase consumer unit would be rated at 18.40 kVA, leaving (I presume) 36.60 kVA for the 3-phase, once this is balanced (how is balancing achieved in this sort of situation, by the way?).
I will also, by then, need a powerful EV charging wallbox. An 11 kW one is for 3-phase only, as would be a 22 kW electric boiler (heat pump technology is not suitable for our home). If these two appliances consume 33 kVA, the 3-phase will be used to over 80% of its capacity, but it could be arranged that the two would never be on at the same time.
The 23 kVA single-phase circuit, with capacity reduced to 18.4 kVA, will need to carry extra loads:-
Cooker (12 kW maximum, 7 kW diversity), 3 kW convector heater.
I have done calculations of the peak consumption of the circuit as it stands now. I need to be confident that these are reasonably realistic, so that I can add the extra loads to the existing ones, and calculate the much higher peak consumptions with the extra loads added. I need to know if the total is likely to be within the reduced 18.40 kVA capacity of this circuit.
If this is relevant (please see below), the additional appliances mentioned for the single-phase, and both those for the 3-phase, have power factor 1.
As regards the existing load on the single-phase circuit, if a p.f. should be applied, it should be reasonable to use 0.8.
To work out first the load on the increased-load circuit as regards the its capacity/the capacity of the cutout fuse, I need to know if I should increase the kW of the total existing load by 1/0.8, so as to include apparent as well as real current, and get a figure in kVA. Or should use the total kW. At that point I would add the extra loads of the cooker and convector heater, as kVA and kW are identical.
Calculating Amps using kVA increases the load on the existing circuit by 25% if p.f. is 0.8, so, after adding the extra proposed loads, there is unsurprisingly considerably more "headroom" left in the circuit capacity if I calculate using kW.
I suspect that kW is the correct basis to use, because apparent current passes back into the grid after passing through the circuitry of an appliance. An appliance may draw, say. 10 Amps. If its p.f. is 0.8, 2 Amps are returned to the grid instantaneously as the 10 Amps are drawn. This is why a Watt/hour meter records using the voltage times the net current used up by loads, and so reads in kWh and not kVAh.
So I suspect that the cutout fuse draws the net current (full current less apparent current).
Which should I use for my calculation: kW or kVA? If the answer is kVA, then, in view of my comments just above, where have I misunderstood things?
I've tried to find an answer to this, but can't find any focussed guidance.
Can forum members enlighten me reliably, please?
Carl
Only about 13% of my total energy consumption is electricity. The remaining 87% is natural gas, supplying the following appliances (kW figures are net output power):-
22 kW boiler, 3 kW fan-flued convector heater. 8 Kw cooker.
After (if?) natural gas is turned off some time in the 2030s I can have 3-phase installed (at vast cost) to give me total kVA 55.15 at 230 Volts. As you can see, this offer is tied to reducing the supply capacity per phase to 80 Amps. So a connection from one phase (and the neutral) to my existing single-phase consumer unit would be rated at 18.40 kVA, leaving (I presume) 36.60 kVA for the 3-phase, once this is balanced (how is balancing achieved in this sort of situation, by the way?).
I will also, by then, need a powerful EV charging wallbox. An 11 kW one is for 3-phase only, as would be a 22 kW electric boiler (heat pump technology is not suitable for our home). If these two appliances consume 33 kVA, the 3-phase will be used to over 80% of its capacity, but it could be arranged that the two would never be on at the same time.
The 23 kVA single-phase circuit, with capacity reduced to 18.4 kVA, will need to carry extra loads:-
Cooker (12 kW maximum, 7 kW diversity), 3 kW convector heater.
I have done calculations of the peak consumption of the circuit as it stands now. I need to be confident that these are reasonably realistic, so that I can add the extra loads to the existing ones, and calculate the much higher peak consumptions with the extra loads added. I need to know if the total is likely to be within the reduced 18.40 kVA capacity of this circuit.
If this is relevant (please see below), the additional appliances mentioned for the single-phase, and both those for the 3-phase, have power factor 1.
As regards the existing load on the single-phase circuit, if a p.f. should be applied, it should be reasonable to use 0.8.
To work out first the load on the increased-load circuit as regards the its capacity/the capacity of the cutout fuse, I need to know if I should increase the kW of the total existing load by 1/0.8, so as to include apparent as well as real current, and get a figure in kVA. Or should use the total kW. At that point I would add the extra loads of the cooker and convector heater, as kVA and kW are identical.
Calculating Amps using kVA increases the load on the existing circuit by 25% if p.f. is 0.8, so, after adding the extra proposed loads, there is unsurprisingly considerably more "headroom" left in the circuit capacity if I calculate using kW.
I suspect that kW is the correct basis to use, because apparent current passes back into the grid after passing through the circuitry of an appliance. An appliance may draw, say. 10 Amps. If its p.f. is 0.8, 2 Amps are returned to the grid instantaneously as the 10 Amps are drawn. This is why a Watt/hour meter records using the voltage times the net current used up by loads, and so reads in kWh and not kVAh.
So I suspect that the cutout fuse draws the net current (full current less apparent current).
Which should I use for my calculation: kW or kVA? If the answer is kVA, then, in view of my comments just above, where have I misunderstood things?
I've tried to find an answer to this, but can't find any focussed guidance.
Can forum members enlighten me reliably, please?