Thanks for the additional comments.

As to how/why the cable was installed as it was, that was before I got involved, but I gather the customer bought the cable and asked the builder to put it in before it was too late. Possibly the builder knows it was not done properly, or possibly just doesn't understand, as already mentioned.
 
Were all knocking the builder here, but what if the homeowner has put his garden fork through this cable, The OP did say that the cable passes through newly finished plant beds?? You could still blame the builder to a certain extent mind, for not burying the cable to a suitable depth!! lol!!
 
Give them your opinion of where the fault is, ohms one end, ohms other end, cable length, % etc and let them argue with the builders.

Boydy
 
I've already indicated the fault is approx. 1/8 from the end at the CU, which puts it pretty much at the boundary where it exits the extension and enters under the brick-built raised beds, but there is quite a margin of error in this (a 0.03 Ohm reading, with careful nulling), which is where I began. Inside, the builders are at fault, outside then there are some landscape gardeners who did the flower beds that might be at fault. Yes, cutting at the boundary will give some answers, but there is so little of the cable accessible, and depending on which part is damaged, the owner still has thoughts of reusing the non-damaged part, which is why I didn't cut it to check so far.
 
Whoever laid it is at fault. Obviously not at the correct depth or adequately protected. There should have been no digging into it as tape should be buried about 6 inches down to warn it's there.
Sorry, but no excuses here from whoever did it.
 
have you tried exposing cable outside of extension and give it a good pull to see if it moves if its only 8mtr you might be able to pull enough to see damage (unless its cast in concrete)
 
have you tried exposing cable outside of extension and give it a good pull to see if it moves if its only 8mtr you might be able to pull enough to see damage (unless its cast in concrete)

The 8 metres is set into a concrete slab, the other 50+ metres is buried!! I'd like to see you, or even King Kong, to pull more than an inch, and then only if you're very lucky!! lol!!
 
Update: After some delay, the builder finally brought his electrician along and they replaced the damaged SWA section - the first approx. 8m, that goes under the concrete floor, and probably got damaged when laying the concrete.

There is a nice resin sealed joint to the rest of the cable. However, there is no continuity of the steel armour, only the 3 cores (which all test fine). Yes, I can earth the two halves of the SWA outer from each end separately, since one core will be earth. But should I really be insisting the joint is remade?
 

Reply to Locating an SWA fault? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
382
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
963
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

I assume said contractor is part of a Part P scheme (NICEIC, Napit, few others..) in which case complain to them. They'll investigate (in theory)...
Replies
10
Views
918
Sounds more positive.
Replies
8
Views
631

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top