Well I have tested continuity of each core, testing 2 cores in turn, 0.23 Ohm per any two cores for the approx. 65m length. And IR >1999 MOhm between any two cores. I just think the guy didn't bother to connect the armour, the customer has left a message for him asking why not.
 
Update: After some delay, the builder finally brought his electrician along and they replaced the damaged SWA section - the first approx. 8m, that goes under the concrete floor, and probably got damaged when laying the concrete.

There is a nice resin sealed joint to the rest of the cable. However, there is no continuity of the steel armour, only the 3 cores (which all test fine). Yes, I can earth the two halves of the SWA outer from each end separately, since one core will be earth. But should I really be insisting the joint is remade?

It's OK then, if you don't want more disruption. Earth it and test.
 
Update: After some delay, the builder finally brought his electrician along and they replaced the damaged SWA section - the first approx. 8m, that goes under the concrete floor, and probably got damaged when laying the concrete.

There is a nice resin sealed joint to the rest of the cable. However, there is no continuity of the steel armour, only the 3 cores (which all test fine). Yes, I can earth the two halves of the SWA outer from each end separately, since one core will be earth. But should I really be insisting the joint is remade?

Get the builder to bring his sparky back again?
 
Sounds like some Electrical Trainee has done his first resin joint.

I think the guy has been around some time, probably not a Electrical Trainee, just has some odd ideas about regs. For example, he also said to the customer the SWA should be connected directly into a Henley block from the meter tails (all 65m of it), with no protective device.
 
this tale of electrical woe is chock full of fail.

of course you should connect the swa's together in the joint , thats what the spring clips and braiding are for.

of course you dont connect the swa direct to henley blocks , you use glands and a switch fuse.

these clowns should seriously step away from the work area lol.
 
I think the guy has been around some time, probably not a Electrical Trainee, just has some odd ideas about regs. For example, he also said to the customer the SWA should be connected directly into a Henley block from the meter tails (all 65m of it), with no protective device.

No switch fuse? crikey!!

- - - Updated - - -

shot gun biff lol
 
I think the guy has been around some time, probably not a Electrical Trainee, just has some odd ideas about regs. For example, he also said to the customer the SWA should be connected directly into a Henley block from the meter tails (all 65m of it), with no protective device.

Not actually an electrician then, just someone with a little knowledge "who's been doing it a long time". See it all the time...just because they haven't killed anyone yet, they think it makes them "experienced". pff
 
I think the guy has been around some time, probably not a Electrical Trainee, just has some odd ideas about regs. For example, he also said to the customer the SWA should be connected directly into a Henley block from the meter tails (all 65m of it), with no protective device.

One things for sure be he a electrical trainee or not, ....he aint no electrician!!!
 
This forum is probably just a microcosm of what's occurring out there in the electrical world.
There seem to be quite few tales of Woe like this on here, scale it up to encompass the whole electrical activity in country...
I'll leave the rest to one's imagination! :)
 
This forum is probably just a microcosm of what's occurring out there in the electrical world.
There seem to be quite few tales of Woe like this on here, scale it up to encompass the whole electrical activity in country...
I'll leave the rest to one's imagination! :)

You're absolutely right. See it nearly every job I visit. That's what makes it harder for us to do things properly, as all we hear is "well, it's worked ok like that for years..."
 

Reply to Locating an SWA fault? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
961
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

I assume said contractor is part of a Part P scheme (NICEIC, Napit, few others..) in which case complain to them. They'll investigate (in theory)...
Replies
10
Views
918
Sounds more positive.
Replies
8
Views
631

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top