Location of Main Equipotential Bonding | Page 2 | on ElectriciansForums
Discuss Location of Main Equipotential Bonding in the UK Electrical Forum area at ElectriciansForums.net
Dalimo
Surrey
Evening All,
Gone to look at a rewire of a flat. Communal cupboard is a 3 phase supply, with 3 cut outs for each of the flats one of which is split for the landlords CCU.
TN-S system, each flat has an old KMF switch which in turn feeds a 16mm twin and earth cable, approx 1970's build.
Main earthing terminal in the cupboard is a 4 way block:
Earth from supply in 1 terminal, flat 1 on its own, flat 2 on its own, flat 3 doubled up with landlords CCU earthing conductor.
The flat in question has MEB to its incoming gas and water main in 10mm and goes back to the earth bar in the existing CCU (an old Wylex BS3036), which is in turn a 6mm supply (from the 16mm twin and earth).
The consumer unit is being moved to another location, and I have suggested a 16mm SWA, with a switch fuse unit in the communal cupboard.
What are people's preferred methods as its a TN-S system:
Main Bonding to new CCU or,
Main Bonding to MET?
However when I get to the MET I have only 1 terminal spare.
If the consensus is to run it back to the MET, is it better to try and arrange with the other two flats to switch them off and put a bigger block in for the all 3 flats, landlord CCU and my MEB conductors,
or put a link in from my 'spare' terminal to a new earth block for the 16mm SWA and MEB conductors.
Its not a question of costs, just want it to look nice, neat and what my options are if the other flats so NO, we don't want to be switched off.
What are my responsibilities with regards to their supply cable if they say OK, testing wise?
Any advice would be helpful.
David
Had an idea......each of the CPC's is about 10 inches long. Was thinking unscrew the block from the backer board but leaving all the conductors still connected, bend over each of the conductors and they are effectively the size of a 12mm conductor slip each of these doubled up conductors into a terminal of an 8 way block.
Still left the original Met but slipped a new one in front of it without having to disconnect anything and giving me the extra ways?
and if their is a fault in one of the flats ,holly F77k !
Tell me about it, think I'm going to do a mix of testing with the wander lead, working out what is what and bonded to what. At the end of the day if I need to arrange switching off the neighbours so be it.
Thanks everyone for your time, glad I am mulling it over now rather than on site on a Friday afternoon.
And just to make things even more fun with it the hallway, corridor and walls are concrete!
Time for a suicide price.
GN8 details where you should bond and the DNO will have a policy document which will be part of your supply agreement.
You should bond all incoming services (that test as extraneous) to a building earth marshalling point at the origin. The size of bond required is related to the size of the supply N.
Additionally, within each unit (individual equipotential zones) you must bond as you would do in any dwelling . However, unless you have a seperate earthing conductor to each flat to supplement the cpc in the 16mm t & e you will be undersized and you will need to seek guidance from your cps operator on how to proceed. The new 16mm swa you propose would be fine
Reply to Location of Main Equipotential Bonding in the UK Electrical Forum area at ElectriciansForums.net
Indeed it would be. But that would mean having 2 things to disconnect instead of one. More margin for error. Of course, any diligent spark would...
loz2754
L
Why would the RCD fail … yes it can happen but then it may not. Without it you have no protection on the TT System
4K