locking a mcb in the on position | on ElectriciansForums
Discuss locking a mcb in the on position in the UK Electrical Forum area at ElectriciansForums.net
Farmelectrics
Wirral
is it allowed to lock a mcb in the on position data centre spark informs me they have mcbs locked in on so no one accidently nocks breaker off i tell him that could be dangerous as the breaker will not trip in fault condition but he tells me that thermally the breaker will still trip anyone come across this your thoughts please chaps
Yes you can lock an MCB in the on position eg fire alarm supply etc. and yes the MCB will still trip in the event of a fault.
Yes both MCBS and MCCB's will still trip when locked in the ON position. The switching mechanism of both, has no direct effect on the protective elements within these devices!!!
I'm not sure about the UK regs but depending on the supply arrangement we'd need to provide another point of isolation for the equipment if the MCB or MCCB was locked in the 'on' position.
Normally, the locking ''ON'' of MCB/MCCB's would only be found on in-house maintained plant or equipment, where the staff responsible would be in possession of the lock key. Can't really see why you would want another point of isolation to be honest, any fault would be cleared by the protective device whether it be locked ''ON'' or not. I guess ...depending on the plant, you could have a local isolator. It would be prudent to have a means of indication (indicator lamps) in such situations, and many of them do, that i've come across!!
You ever been on a big site tony? :carolers: A guy told me when at tech, some old factories would have these isolators that are locked on cause they no load isolators. = switch all load off right down to main isolator
Never seen a ''Locked ON'' Isolator in all the years i've been in the industry, including my years in the industrial sector. For a start, you don't install no load isolators on motor circuits, they will be rated isolators...
You know I have. To lock an isolator "ON" would lead to instant dismisal.
BTW It off load, not no load!
Reply to locking a mcb in the on position in the UK Electrical Forum area at ElectriciansForums.net
Nothing wrong with it. Which manufacturers have you got this information from? What do you mean by trip speed? Fuses and MCBs can operate in the...
davesparks