Went to daughters house to replace a couple of broken sockets and did a Zs and RCD test after replacing. CU was replaced and notice on it said inspected 2015. Plastic dual RCD 30 ma/Main switch 60947-3 isolator. System is TT. (100ma RCD?)
Zs at socket was 11.75 ohms L-PE 2.64 ohms L-N. No bonding present to services. Suggested my daughter might get the council in to check it out. Had a phone call today and electrician said it is all compliant! He also said it disconnects in 0.37ms and I asked to talk to him he would not. He said I was just trying to make money, if only he knew? Apparently he fixed the bonding in a few minutes.
I said to my daughter tell him it should be 0.2 (the property is not cross bonded as in the exception to table 41.1) he said that was the case 20 years ago and I needed to get up to date. Okay!
I must confess to be a little bit taken aback by this and thought I would do a sanity check with the forum members. I do have Amd 3 BS7671 by the way i.e. 2382-15 so I think I am up to date.
Essentially I am of course concerned for my daughter, and what appears to be possibly a cavalier attitude. I told my daughter to get a copy of the report and tests so we await that. Am I being concerned over nothing or just plain stupid??? Tin hat on.
 
Sorry if I've missed something, but B32 won't trip "instantly" with that L-N impedance. Hopefully appliances are protected by 13A fuses but a short in the cabling would cook for a while, I think.
And stepping out on the edge a bit further, I don't think the ring is intact :)
 
Wrong..... if you look below table 41.1, it specifically mentions RCDs.
But if you rely on an RCD for fault protection you must ensure the fault currents are significantly higher than the rated residual current of the RCD.

As RCDs are used for additional protection then the timings for those must comply with table 3A in appendix 3.

Leaving you to ensure that the PSSC of the installation will disconnect the OCPD within the stated times of 41.1.
 
Ok so still, 11.7 ohms Zs on RFC any thoughts? 60898 MCB 32a B
Using a 30mA RCD for earth fault protection then your maximum permitted Zs is 1667 ohms.

But what was the PSSC for the circuit? Only this measurement will tell you if the OCPD will disconnect within 0.2 seconds.

For a 32 amp B type 60898 you need a current of 5x the device rating for a disconnection time between 0.1 and 5 seconds. i.e. 160 amps.
 
Infact looking at one of your earlier posts with you L>N of 2.64 ohms that will give you a fault current of 87 amps which will disconnect in roughly 40 seconds so it will not comply.

How far out in the sticks is her house and what was the voltage reading?
 
I tested a tt system yestersay and the zs at db was 9.11 ohms with ipf of 25a, on the socket circuit i got a zs of 10 ohms and an r1+r2 reading of 0.49 ohms and was told this was fine....i always thought and was taught a tt would give higher readings for a zs than as given in appendix table b6. Now im confused :confused:
 
The higher zs is fine, and dealt with by the application of rcds for fault protection, and in this case since they are 30ma they will also provide additional protection. The curve ball is the 2.64 ohm L-N....generally we assume that if R1+R2 is good then R1+RN would be as well....since the CSA of cpc will be less than or equal to the neutral...but ring finals aside, what specific tests are mandated to check this? Could well be a loose neutral connection, but how are these tested?
Often hear circumstantial evidence that it's always neutrals that burn out or are loose....is it because a loose l or cpc gets picked up during r1+r2 testing, but those pesky neutrals fall by the wayside? Just a thought....
 
Doesn't need to comply across L/N as no values are given for this scenario. We need to know the L/N reading at source.
A different time to comply perhaps?
Reg 434.5.2 says to interrupt fault current before damage has occurred. So we don't need 200ms but we do need to check dis times with adiabatic (?).
 
Compliance should be checked each time the installation is inspected and tested as supply nature and perameters change.

A circuit that complied when designed may not comply now.
 

Reply to Looking for opinion on whether this scenario is compliant in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
717
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
3K

Similar threads

  • Question
There could also be a completely unsuitable junction box embedded within the wall and tiled over or just cables in choc blocks in old accessory...
Replies
6
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top