The Ghost

Went to daughters house to replace a couple of broken sockets and did a Zs and RCD test after replacing. CU was replaced and notice on it said inspected 2015. Plastic dual RCD 30 ma/Main switch 60947-3 isolator. System is TT. (100ma RCD?)
Zs at socket was 11.75 ohms L-PE 2.64 ohms L-N. No bonding present to services. Suggested my daughter might get the council in to check it out. Had a phone call today and electrician said it is all compliant! He also said it disconnects in 0.37ms and I asked to talk to him he would not. He said I was just trying to make money, if only he knew? Apparently he fixed the bonding in a few minutes.
I said to my daughter tell him it should be 0.2 (the property is not cross bonded as in the exception to table 41.1) he said that was the case 20 years ago and I needed to get up to date. Okay!
I must confess to be a little bit taken aback by this and thought I would do a sanity check with the forum members. I do have Amd 3 BS7671 by the way i.e. 2382-15 so I think I am up to date.
Essentially I am of course concerned for my daughter, and what appears to be possibly a cavalier attitude. I told my daughter to get a copy of the report and tests so we await that. Am I being concerned over nothing or just plain stupid??? Tin hat on.
 
A different time to comply perhaps?
Reg 434.5.2 says to interrupt fault current before damage has occurred. So we don't need 200ms but we do need to check dis times with adiabatic (?).
Good point although adiabatic should only be used up to 5s, go far beyond that and the value would be way too conservative.
Not sure how to work it out, i agree with the rest of your post. I feel like we should be sizing it as an overload protection, so as long as the mcb can protect the cable that way it's ok? There's no special case of worrying about exposed conductive parts being live in this case.
 
If there isn't a defect in the DNO supply or the RFC, then the RFC must be very long to get L-N of 2.6 Ohms at an outlet. Either way, the voltage drop would slow down my tea and toast, no good at all !
 
The rcds are providing fault protection
Are they? This is a dual RCD board and if I understand correctly the RCD are additional protection. As this is a TT system why would one not use an up front 100ma RCD for fault protection. I must admit I very rarely if ever encounter TT and if I do usually get it converted to PME so frankly I am not on top of the implications reg wise of TT.
 
Are they? This is a dual RCD board and if I understand correctly the RCD are additional protection. As this is a TT system why would one not use an up front 100ma RCD for fault protection. I must admit I very rarely if ever encounter TT and if I do usually get it converted to PME so frankly I am not on top of the implications reg wise of TT.
30mA rcds offer fault protection for earth faults only and have the added bonus of offering additional protection hence the 2 tests.
1x rating trip within 200ms for circuits upto 32 amps if it’s TT (the standard for bs61008 and 61009 being 300ms) and 5x for additional protection within 40ms.
Your mcbs will be providing short circuit and overload protection only.
It maybe that additional protection via 30mA rcd is required for socket outlets,cables serving a bathroom location and cables buried in walls etc rather than relying on a 100mA rcd which would not comply with the requirements of additional protection and only offers fault protection.
I would not be worrying about your high Zs readings after all it’s a TT arrangement and as your covered for earth faults via the dual rcds in the consumer unit.
what your issue is with the bonding requirements will only be applicable if you have extraneous conductive parts entering the dwelling.
 
Last edited:
Hi - agree.
But any L-E faults before the CU's RCDs will have to clear via the service fuse. And with TT its likely it won't clear and there's risk the installation E could rise. Case of L tail flapping about inside AMD3 CU for example (very unlikely and why tails glands and good workmanship always needed).
 
Hi - agree.
But any L-E faults before the CU's RCDs will have to clear via the service fuse. And with TT its likely it won't clear and there's risk the installation E could rise. Case of L tail flapping about inside AMD3 CU for example (very unlikely and why tails glands and good workmanship always needed).
I like to install an S type rcd rather than the main switch if using a dual rcd board but that’s just my preference on TT arrangements.
 
Yes agreed a plastic consumer unit takes the danger scenario of loose tails touching the enclosure causing a potential hazard, out of the equation
... Although of course there's still the risk of the CU catching fire.
I had a quick leaf through the new OSG in the wholesalers the other day - there's bit in it about countering precisely that situation, but I can't remember the exact details.
 
The higher zs is fine, and dealt with by the application of rcds for fault protection, and in this case since they are 30ma they will also provide additional protection. The curve ball is the 2.64 ohm L-N....generally we assume that if R1+R2 is good then R1+RN would be as well....since the CSA of cpc will be less than or equal to the neutral...but ring finals aside, what specific tests are mandated to check this? Could well be a loose neutral connection, but how are these tested?
Often hear circumstantial evidence that it's always neutrals that burn out or are loose....is it because a loose l or cpc gets picked up during r1+r2 testing, but those pesky neutrals fall by the wayside? Just a thought....

Totally agree
 

Reply to Looking for opinion on whether this scenario is compliant in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
717
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
3K

Similar threads

  • Question
There could also be a completely unsuitable junction box embedded within the wall and tiled over or just cables in choc blocks in old accessory...
Replies
6
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top