Hello
I'm not sure if this is the correct forum area to post this in, apologies if it isn't...
I've been working through some mock questions on-line, and found myself confused by this:
The measured value of loop impedance for a circuit is 0.83ohm.
If the temperature at the time of the test was 20C, and the cable is 70C (factor 1.2) what is the corrected value. Ze = 0.4ohm:
a) 0.43 ohm
b) 0.86 ohm
c) 0.996 ohm
d) 0.916 ohm
I just cant get my head around this!
Any help would be great!
Thanks in advance,
Gary
Basically the temperature correction won't apply to the part external to the installation but only to your cables within the installation. So apply your temperature correction to this part and then you have your adjusted value. (I don't want to just give you the answer.)
Hello
a) 0.43 ohm
b) 0.86 ohm
c) 0.996 ohm
d) 0.916 ohm
Thanks in advance,
Gary
Apply the correction factor stated, to your 0.83 value
Peterborough
Trainee Electrician
loop impedance, temperature, cable factor....
Gary Tollison,
cireland,