Loop test with fluke three wire ?? | on ElectriciansForums
Discuss Loop test with fluke three wire ?? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Can anyone shed any light. Just done loop test with fluke L-N-E setting L-PE. Reading was 8.66 ohms. Have reported high reading to DNO who sent engineer out. He then tested two wire L-E and read 0.13 ohms. this iss not the first time with high reading on my tester and has recently been calibrated. Am I doing something wrong ??
but on the fluke if you don't use three wire it shows error and as well as being in the instructions, most of the time it is not a problem. This is the second time DNO have disputed the reading though
Reply to Loop test with fluke three wire ?? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Hi, Do you have the user guide. If not I will put the link at the end of the mail. May be worth checking that the meter has been set for UK usage...
Having some issues with my companys fluke 1662/1663 tester. Zeroing 2 leads for continuity test we get the value 0.08 which is expected. The issue...