I’ve just carried out a continuity test on a rfc. And I’m getting a lower earth resistance Reading than the reading on both the live and neutral wires.
its a circuit in a house converted into two flats and the circuit is wired in 2.5/1.5 twin and earth.

Live and neutral are both 0.46
earth is 0.37, obviously I expect earth to be 1.67x higher not lower.

Ive opened up every socket and all looks fine, I’ve also done continuity with Live and neutral and live and earth connected, and the figures for these are spot on at every socket. (From the terminals)

All the wires are out of the cu, and there’s not a boiler connected to the rfc. It’s all normal twin and earth into metal back boxes there’s no metal conduit etc

The ze for the circuit is fine.

I assume it must be a parallel earth some where but no idea where or how, anyone got any ideas because I’m at a loss and I hate things not being right lol.

I assume as everything else is okay I just need to accept the lower reading.
 
Hi,if you had one hidden accessory or JB,which bridges the ring somewhere,and it had a poor connection on the cpc,you could get this....

You could clip a signal generator on the disconnected cpc,and CAT the whole gaff,to see if there are unexpected cable runs....

Now and again,in circumstances like this,i find that not worrying or thinking about it,works wonders 🙂
 
Hi,if you had one hidden accessory or JB,which bridges the ring somewhere,and it had a poor connection on the cpc,you could get this....

You could clip a signal generator on the disconnected cpc,and CAT the whole gaff,to see if there are unexpected cable runs....

Now and again,in circumstances like this,i find that not worrying or thinking about it,works wonders 🙂
To be honest that’s kind of where I’m at now lol. At the end of the day it’s not a safety issue.
 
Could be a loose connection at one of the sso???

A bad connection would surly give a higher reading not lower. R1 and r2 are exactly the same they both can’t have a equally bad connection to give higher readings!!’
Yes I realised that after I posted sorry my bad
 

Reply to Low earth resistance continuity test in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
429
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

I was at the other end of the results spectrum today. As I was driving home I had a call from my "Mrs Richards from Fawlty Towers" lady, very deaf...
2
Replies
20
Views
1K
  • Question
I may have been mistaken regarding TT I will look into that, thank you for the valued reply, but in general I stick to my post, a good topic for...
2
Replies
24
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top