Hi Everyone

Just a question bothering me as you cannot do Insulation resistance test on smoke detectors as they can become damaged so obviously smoke detectors are sensitive but they are also installed on lighting circuit so if perform low insulation resistance test 250V between Live and earth would that be safe or still they should be disconnected first or if not possible then it is a limitation ?
 
SOme of these are badly fitted and I sometime avoid taking them down incase if they dont fit back properly so was wondering if I could test with low IR by using Line,Neture together with earth
 
You can test at 250VDC but the internal circuitry of the heads will probably give you poor readings.

Best to do line/neutral to earth, I tend to do 250VDC first in case of current using equipment still fitted that might throw your results such as switched mode power supplies, the 500VDC if I'm happy to proceed.

I'm guessing this is for periodic inspection rather than new installation?
 
SOme of these are badly fitted and I sometime avoid taking them down incase if they dont fit back properly so was wondering if I could test with low IR by using Line,Neture together with earth

If they’re badly fitted I’d still want to take them down before testing, then code accordingly and rectify where needed.
 

Reply to Low Insulation resistance test on smoke detectors in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
521
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
2K

Similar threads

Thanks, I was hoping someone could confirm whether it was odd or not. I've done a fair bit of insulation testing but only on a small number of...
Replies
4
Views
298
  • Question
There can be a few reasons for low L+N -> E readings: Connected equipment is leaking. By design, or just old/damp SPD are connected (but there...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top