Hey people,
I did some testing for a sporadic RCD trip this week.
The customer did some playing about and narrowed it down to the garage.
Tested the garage circuits and all were good. Tested the feed and found with the CPC still in the bar I got 0.076 meg but when I pulled it out the fault cleared.
All I can think is it's chaffed through somewhere like maybe on a CH pipe? but just thought I would check I'm not doing something stupid before pulling in a new feed.
Cheers,