Hi. I don't know if anyone can help or shed any light on this one.
I installed a new circuit in my sons garage. 2.5 T&E clipped direct, 4x metal clad sockets and back boxes.
I haven't terminated it into the CU yet as I need to get a RCBO.
I just got everything in place and did dead tests.

End to end L 0.21Ohm
N 0.21Ohm
E 0.02 Ohm

IR >1000 Mohm

There is nothing connected in the board so no parallel paths.
I had my yearly assesment today and I asked the assessor and he couldn't think of why it would be so low.
Any one any ideas?
Thanks
 
Hi. I don't know if anyone can help or shed any light on this one.
I installed a new circuit in my sons garage. 2.5 T&E clipped direct, 4x metal clad sockets and back boxes.
I haven't terminated it into the CU yet as I need to get a RCBO.
I just got everything in place and did dead tests.

End to end L 0.21Ohm
N 0.21Ohm
E 0.02 Ohm

IR >1000 Mohm

There is nothing connected in the board so no parallel paths.
I had my yearly assesment today and I asked the assessor and he couldn't think of why it would be so low.
Any one any ideas?
Thanks


Poor connection on your MFT?
 
They haven't put in a 10mm CPC in the T+E have they?

Honestly this defies logic. You obviously have a ring on your r1 rn and so by rights your smaller CPC should be higher on r2.

All I can think of it start to break the ring down, it's only 4 sockets and test the cable from CU to Socket 1 and then Socket 1 to 2 and go round the ring
 
Thanks for the replies.
(Hightower) No parallel paths. End to end on drum, I will try that. It was a new 100Mt roll.
(Steve) It's a double garage, the CU is in the garage. so total ring about 15/20mts? They are fixed to a breeze block wall.
(malcolm) Will do, I will be going back there next week to finish off, so I will try that.
 
Thanks for the replies.
(Hightower) No parallel paths. End to end on drum, I will try that. It was a new 100Mt roll.
(Steve) It's a double garage, the CU is in the garage. so total ring about 15/20mts? They are fixed to a breeze block wall.
(malcolm) Will do, I will be going back there next week to finish off, so I will try that.
Metal sockets? if so remove the front plates from the back box and dis the fly lead (if you have one) and re test r2
 

Reply to Low R2 in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
270
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
766
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
771

Similar threads

  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top