Hi. I don't know if anyone can help or shed any light on this one.
I installed a new circuit in my sons garage. 2.5 T&E clipped direct, 4x metal clad sockets and back boxes.
I haven't terminated it into the CU yet as I need to get a RCBO.
I just got everything in place and did dead tests.
End to end L 0.21Ohm
N 0.21Ohm
E 0.02 Ohm
IR >1000 Mohm
There is nothing connected in the board so no parallel paths.
I had my yearly assesment today and I asked the assessor and he couldn't think of why it would be so low.
Any one any ideas?
Thanks