You were warned.Stop the bickering and keep the thread on topic.
banstick for jenny66 ?
;-)
If that is the case then that would be supplementary bonding which, unless in a bathroom or similar location, is not required.The 0.05 value is the value below which potential difference should be, between simultaneously accessible extraneous conductive parts. Example of which is a gas pipe and a water pipe next to each other. Test between the two.
Even if both are 10mm bonded individually back to MET, if the difference between the two is greater than 0.05 then they need to be bonded to each other.
But that is, indeed, what is required in my old copy of GN3 (has it changed?).The 0.05 figure is not a value to be achieved between MET and bonding point taking into account the value of resistance of the cable.
If that is the case then that would be supplementary bonding which, unless in a bathroom or similar location, is not required.
But that is, indeed, what is required in my old copy of GN3 (has it changed?).
So - if still required, it must be agreed that it is not possible to achieve this with a conductor whose own resistance is greater than 0.05Ω.
It also states that supplementary bonding conductors must have a resistance of 0.05Ω or less.