I am perfectly willing to accept thanks for the information given in Voltz's posts if you think it is valuable, after all I missed much of the Wales Vs France game to explain it to him in detail!
First time i've read this thread but the most amusing point of it for me is the fact post #14 explained the 0.05 value and it seems to have taken a day for many others to catch up....
well then always keep an open mind. as soon as you see turd at an install....it is an existing bonding cable, was gonna change the board for an assessment but now i'll need this to be sorted. p.s. the cowboy who installed this bodged quite alot so dunno what is going on
well then always keep an open mind. as soon as you see turd at an install....
The 0.05 relates to the bonding connection, not the conductor length. This is to conform the clamp is connected to the conductive part with a low resistance joint. (i.e. paint removed from pipe). This relates over to the 0.1 + R of lead used in the COP for portable appliance testing, as there are 2 points of connection (0.05+0.05=0.1)
The purpose of the main protective bonding conductor is to equalise the potential, so we only see the volt drop (touch voltage) of the R2 conductor, between conductive parts under fault conditions. If no bonding is present, we will see the volt drop of the R2 conductor, plus the volt drop of the external earth. Obviously this will be greater in TT installations, due to the higher resistance in the earth electrodes.
a few of us have already stated, the fact that it's over 0.05 on a relatively short run is indicating that it's not continuous and needs investigating.
The only way it can be over 0.05ohms is if there is a fault / most likely a high resistance joint, therefore if it's over that figure (or at least over it significantly) then it can not just be left, it should be investigated and rectified.he may well have a fault be he's asking does it have to be 0.05ohms or under the answer is NO
he may well have a fault be he's asking does it have to be 0.05ohms or under the answer is NO