Hi been to a job wants a shed wired, about fifty meters away from the house, my concern is the bonding to the services, not good and near impossible to route to within 600mm of the stop cock/gas meter, my question is could i bond the pipes at the upstairs meter? I know what the regs state but its not if not practicable to tear the house apart to do so? Tns, currently 2,5mm to the main earth, bonding same to god knows where many thanks
 
You are trying to ensure that the bonding is connected as close as possible to the place where the 0V reference starts and to ensure that no modifications before the bonding clamp can leave an unbonded extraneous part.
It is possible that the combi boiler is acceptable but not likely, however you can see the pipework run and must make the call.
 
As Richard said ^^^^^
Although its best practice to connect the bonding within 600mm at point of entry, sometimes this is not possible/practical. In these scenarios you are required to determine the best possible connection point and then make a note on your EICR.
 
Sorry lol i suppose my point being if i was to upgrade the main bonding as well as install the shed supply but am unable to access service pipes where they enter the property, or just ignore the bonding and just note it on the eic?
 
Sorry lol i suppose my point being if i was to upgrade the main bonding as well as install the shed supply but am unable to access service pipes where they enter the property, or just ignore the bonding and just note it on the eic?
You mentioned 2.5mm2 bonding conductors, is that correct?
 
I mention the plastic pipes as this can change the needs for bonding. I've been in a recent new build with plastic incoming water main that was not bonded. I did confirm the odd copper pipes under the sink etc were not extraneous and just noted it on my cert.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Port Talbot
Business Name
Baglan electrical services

Thread Information

Title
Main bonding problem again
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
13
Unsolved
--

Advert

Thread statistics

Created
Pico1978,
Last reply from
Midwest,
Replies
13
Views
1,527

Advert

Back
Top