no i want to do it but clients wonder why you want to run an earth wire right through their house or right round it when all they have done is move their boiler
 
The pipes may or may not introduce an earth potential.The fuel supply to the boiler may have a bearing.If a metallic oil or gas line from an external source feeds the boiler and does not enter the building then that service would not require main bonding.However the pipes from the boiler into the building may intoduce an earth potential via the fuel service and so would require main bonding at the point of entry.
If the fuel service originates from within the building and is main bonded within the building,and the boiler is on a concrete plinth,then the pipes may not introduce an earth potential and so wont require bonding.
IMO though it would be difficult to establish that the pipes will never introduce an earth potential and so I always main bond the flow and return pipes at the point of entry if they are from an external boiler on the deck.
 
Last edited by a moderator:
Hi,

You can always test the pipes to see if they're extraneous and require bonding.:)

Rcp> (Uo/Ib) - Ztl


Where:

Rcp is the resistance between the conductive part and the MET in ohms


Uo is the nominal voltage to Earth in volts.(230)


Ib is the value of current through the body in amperes that should not be exceeded. (I would err on the side of caution and use 10 mA)

Ztl is the impedance of the human body in ohms. The value suggested in DD IEC/TS 60479 is 1000 ohms where Uo is 230 V (50 Hz) under dry or wet conditions.

So,

Rcp = (230 / 0.010) - 1000

Rcp = 22,000 ohms (22 kohms)

So, if the resistance between the pipes and the MET is above 22 kohms, they would not be considered extraneous and would not require bonding.

The NICEIC recommend using a 30mA current, which would give you a threshold of 6667 ohms (6.7 kohms) and say that above this wouldn't require bonding - but I'd sooner be a bit more cautious:)

So, bottom line, if you don't know if it requires bonding...........test it.;)

http://www.electriciansforums.net/e...ical-regulations/16558-extraneous-yes-no.html
 
Last edited by a moderator:
Hi WayneL. Very useful post.
When you say test to the MET do you mean with only the main earth conductor connected or with bonding conductors connected as well (I presume that all cpcs are removed to avoid confusion). I ask because if the pipe is connected to another pipe which is bonded you would get a resistance value below 22 kohms. If that was the case what value of resistance would be low enough to not have to bond the pipe.
 
Hi SJM,

I know the point that you are trying to make.

I think if it's already bonded (indirectly), then you would expect the reading to be really low - you'd be looking for the negligible 0.05 ohms - which would mean that it was already part of the 'equipotential zone'.

I think this test is more for 'stand-alone' metalwork or pipes that you can't decide whether it's extraneous or not.

Could be an idea to do what you said and remove other bonding from the MET first, so that you are just testing the particular pipe that you are interested in - otherwise complex installations could give dodgy readings from parallels.

I personally haven't had to put this to the test - with the jobs I've done it's been pretty obvious on what needs bonding and what doesn't.
I might have a little play with my meter when I get some spare time and see what kind of results I get.:)
 
As above.....testing to establish whether or not an incoming service is an extraneous conductive part is much harder in practice than theory due to parallell paths from connected pipes/wiring.
The only way in practice would be to test the pipes coming from an already installed boiler into the building before they were connected to any other pipework within the building.......not likely to be an option.
 
Thanks for the reply WayneL, pretty much what I thought then. I suspect the test is more directed towards new installations and therefore existing installations give rise to problems, as wirepuller has posted above.
 
Last edited by a moderator:
Does anyone agree...Regardless of the regs..If you run a separate CPC and bond all metalwork,then crossbond within the premises,you have covered yourself...bearing in mind,..PME/TNC-S is a money saver for distribution companies...All Earths should be independent,even if connected to Neutral at the Star,they should have their own independent means of flow and escape,without jeapordising or Infiltrating any part of the system..Safety first!!!!!

As said previously...You can always test between main earth and all other pipework/extraneous to see if your continouity bleeps!!!!
 
Last edited by a moderator:
Well you could....but you could make youself a lot of unecessary work as well.
Main bonding is to incoming services is essential,supplementary bonding in special locations (only as defined in 7671) may be required....anything else is a waste of time and money.
 

Reply to main bonding to external boilers in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar threads

Indeed it would be. But that would mean having 2 things to disconnect instead of one. More margin for error. Of course, any diligent spark would...
Replies
6
Views
609
loz2754
L
  • Question
4-5 hours for 150? no chance, this is 2024, 150 for 2 hours maybe, that said an hour seems pretty quick, not sure he did the job right
2
Replies
23
Views
2K

Recommended Sponsor News

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top