MAIN EARTH BONDING domestic installation | on ElectriciansForums

Discuss MAIN EARTH BONDING domestic installation in the Domestic Electrician Forum area at ElectriciansForums.net

P

piz

Hello
When we are asked to change a CU i have been told on pme and tns the main earthing conductor is the responsibilty of the electricity board.
so if this is the case why is a 16 mm earth sold on packs of 2meter tails?,
example change board 25mm tails or 16mm if 80amp main fuse 10mm to gas and water but only sometimes 4 or 6 mm main earth do we just record this on an EIC
Cheers
 
I'm wondering when the thread title will be relevant to the thread

As said in post 2 - the DNO must supply a suitable earth - if they cant provide one within regs then you must supply a TT rod!
The DNO must only make an earth available (if they can) and it is your job then to ensure the cable between the termination of the DNO and the CU is upto regs
 
Pretty pointless exercise then, to have an earth rod that's not buried!! lol!!!

I know your taking the **** - its driven into the ground but the top is exposed - therefore not buried and not protected against mechanical protection - regs states 25mm - I cant be bothered to get OSG or BGB out for the Reg number
 
I know your taking the **** - its driven into the ground but the top is exposed - therefore not buried and not protected against mechanical protection - regs states 25mm - I cant be bothered to get OSG or BGB out for the Reg number
Nicholas I think you have mis-read the OSG.

it says min 25mm if buried but not protected against corrosion

2.5mm if not buried but protected against corrosion and mechanical damage,
4mm if not protected and not buried

 

Reply to MAIN EARTH BONDING domestic installation in the Domestic Electrician Forum area at ElectriciansForums.net

Similar Threads

  • Question
This depends on a number of factors. If you are using the table 54.7 method then it will need to be 16mm. If, however, you are calculating the...
Replies
6
Views
4K
davesparks
D
Yes the first bit is just standard wiring, TNS lead cable into cut-out, cut-out to meter, meter to DP isolator, top of isolator is sealed as per...
Replies
8
Views
945
  • Question
Thanks for the explanation, That's clears up the confusion then. I was worried that I'd been installing insufficient equipment!
Replies
7
Views
2K
  • Question
Actually I hadn't. I've taken on board everyone's comments, thank you.
2
Replies
26
Views
8K
  • Question
Hi there, long time lurker, first time poster here. Straight down to it.. A friend asked me to add some sockets and additional lights to a small...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks