Hello
When we are asked to change a CU i have been told on pme and tns the main earthing conductor is the responsibilty of the electricity board.
so if this is the case why is a 16 mm earth sold on packs of 2meter tails?,
example change board 25mm tails or 16mm if 80amp main fuse 10mm to gas and water but only sometimes 4 or 6 mm main earth do we just record this on an EIC
Cheers
 
Pretty pointless exercise then, to have an earth rod that's not buried!! lol!!!

I know your taking the **** - its driven into the ground but the top is exposed - therefore not buried and not protected against mechanical protection - regs states 25mm - I cant be bothered to get OSG or BGB out for the Reg number
 
I know your taking the **** - its driven into the ground but the top is exposed - therefore not buried and not protected against mechanical protection - regs states 25mm - I cant be bothered to get OSG or BGB out for the Reg number
Nicholas I think you have mis-read the OSG.

it says min 25mm if buried but not protected against corrosion

2.5mm if not buried but protected against corrosion and mechanical damage,
4mm if not protected and not buried

 
542.3.1:
Protected against corrosion and mechanical = 2.5mm copper
Protected against corrosion and not mechanical = 16mm copper
Not Protected against corrosion and not mechanical = 25mm copper

Most properties in Pembrokeshire with TT are not protected against corrosion or mechanical protection so must be 25mm

To terminate 25mm into a CU is a pain I had to split the cable to 4/3 wires and terminate that way over 2 connections - NAPIT said that was the best way
 
542.3.1:
Protected against corrosion and mechanical = 2.5mm copper
Protected against corrosion and not mechanical = 16mm copper
Not Protected against corrosion and not mechanical = 25mm copper

Most properties in Pembrokeshire with TT are not protected against corrosion or mechanical protection so must be 25mm

To terminate 25mm into a CU is a pain I had to split the cable to 4/3 wires and terminate that way over 2 connections - NAPIT said that was the best way

That reg refers to the cable being buried directly in the ground, see the extract from the OSG I posted earler
 
Either way in Pembrokeshire its not possible because all the rods have been concreted to make a path - i will take the trunking idea into consideration next time
 

Reply to the thread, titled "MAIN EARTH BONDING domestic installation" which is posted in Domestic Electrician Forum on Electricians Forums.

Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Daily, weekly or monthly email

Back
Top