P

piz

Hello
When we are asked to change a CU i have been told on pme and tns the main earthing conductor is the responsibilty of the electricity board.
so if this is the case why is a 16 mm earth sold on packs of 2meter tails?,
example change board 25mm tails or 16mm if 80amp main fuse 10mm to gas and water but only sometimes 4 or 6 mm main earth do we just record this on an EIC
Cheers
 
542.3.1:
Protected against corrosion and mechanical = 2.5mm copper
Protected against corrosion and not mechanical = 16mm copper
Not Protected against corrosion and not mechanical = 25mm copper

Most properties in Pembrokeshire with TT are not protected against corrosion or mechanical protection so must be 25mm

To terminate 25mm into a CU is a pain I had to split the cable to 4/3 wires and terminate that way over 2 connections - NAPIT said that was the best way
 
542.3.1:
Protected against corrosion and mechanical = 2.5mm copper
Protected against corrosion and not mechanical = 16mm copper
Not Protected against corrosion and not mechanical = 25mm copper

Most properties in Pembrokeshire with TT are not protected against corrosion or mechanical protection so must be 25mm

To terminate 25mm into a CU is a pain I had to split the cable to 4/3 wires and terminate that way over 2 connections - NAPIT said that was the best way

That reg refers to the cable being buried directly in the ground, see the extract from the OSG I posted earler
 
542.3.1:
Protected against corrosion and mechanical = 2.5mm copper
Protected against corrosion and not mechanical = 16mm copper
Not Protected against corrosion and not mechanical = 25mm copper

Most properties in Pembrokeshire with TT are not protected against corrosion or mechanical protection so must be 25mm

To terminate 25mm into a CU is a pain I had to split the cable to 4/3 wires and terminate that way over 2 connections - NAPIT said that was the best way


The PVC sheath is the protection against corrosion. Bare copper conductor is the type of cable not protected against corrosion... I wouldn't use 16mm for a domestic UK TT system with an Ra value hovering around 200 Ohms!! lol!!
 
Either way in Pembrokeshire its not possible because all the rods have been concreted to make a path - i will take the trunking idea into consideration next time

Shame they didn't install a concrete earth rod pit on the rod and buried the earth conductor in the path too!! Why not run this cable in a metal of heavy duty PVC conduit between rod and where it enters the house, even better chasing the cable into the path. Surely got to be better than a a cable running across a pathway??
 
Nicholas I have used a Max csa of 16mm before where there is no alternative (or at least a cheap alternative) but never 25mm on a domestic TT, as I say I usually just use 10mm simply because I carry this size for main bonding purposes anyway.
 

Reply to MAIN EARTH BONDING domestic installation in the Domestic Electrician Forum area at ElectriciansForums.net

Similar Threads

  • Question
This depends on a number of factors. If you are using the table 54.7 method then it will need to be 16mm. If, however, you are calculating the...
Replies
6
Views
4K
davesparks
D
Yes the first bit is just standard wiring, TNS lead cable into cut-out, cut-out to meter, meter to DP isolator, top of isolator is sealed as per...
Replies
8
Views
945
  • Question
Thanks for the explanation, That's clears up the confusion then. I was worried that I'd been installing insufficient equipment!
Replies
7
Views
2K
  • Question
Actually I hadn't. I've taken on board everyone's comments, thank you.
2
Replies
26
Views
8K
  • Question
Hi there, long time lurker, first time poster here. Straight down to it.. A friend asked me to add some sockets and additional lights to a small...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks