This was my thinking - That's why I am wondering where the main incoming supply is. Whether there is one main supply cable split to individual meters for each flat or if they all have individual cables. Round my way especially its unusual to get flats that all have an individual supply cable coming into them. They normally have one massive supply cable that feeds meters for each flat (That probably makes very little sense to people reading but its clear in my head!).
A gas pipe or water pipe should not be used as a means of main earthing for one common sense reason, the same reason the behind the BRB regulation. Irrespective of whether you get a good Ze measurement or not you can't guarantee that this will always be the case because water/gas companies can and do disrupt/upgrade their supply pipe. ie to plastic pipes
Lol, but was rewired in 1968 by YEB using the same regs I fear. Meter board was held against wall of cellar by a 4" x 4" chump of wood jammed in there.
Possibly not - owned a house in Leeds from the Victorian era where main earth was gas pipe - clamped on the customer side of the meter too....
Had similar thing in my house. There was no earthing conductor.
Only path to earth for the entire property was via the bonds to gas & water mains.
Gas bond was after the meter andf the incoming water was plastic.
o dear
I wasn't talking about an earth fault, by the way.
I was talking about the normal operating current taking this path as oposed to travelling down the neutral(of higher impedance)
Huh? Why would any current other than slight leakage be flowing in the earth in normal operating circumstances?
Both conductors are going to be completely separate upstream until you hit the supply in a TN-C-S system, so surely unless you have a neutral-earth short circuit then there would be no path for the current to get on the earth? :)
But if you bond the gas pipe (with the 0.19 ohm Ze) to the MET, the MET is connected to the neutral at the service head.
So when the normal operating current of the installation flows down the neutral to the service head, it has a choice of path back to the transformer......down the neutral (Ze 0.35) or down the Earthing conductor/Bonding conductor/gas pipe (Ze 0.19).
Where do you think most of it will go?:)
This is why losing the supply neutral on a PME (PEN) system is so worrying.
And this is why I said 0.19 was awfully low for a gas pipe.
You will always get some current flowing down the parallel paths, but it shouldn't be anywhere near that amount.:)
Hmm, I like you, you make me think!! :D
I doubt very much that the earth is actually 0.19 ohms, as it is just a large earth electrode, so methinks the test has been wrong or this is due to parallel paths somehow...
I agree with losing the neutral on a PME supply, but that's why it's an ME and not just an E.
I think Des probs hit the nail on the head with post #15
My thoughts exactly.....If you have to ask whether it is acceptable to use a gas pipe as a main earth you do not have sufficient knowledge to be carrying out a PIR.
*******Removed******* I knew it wasn't acceptable for BS7671:2008 but the wiring was over 60 years.
So you haven't been around for nearly 3 years, and come back having a rant at a respected member, for making what was a valid observation!!
See you in another 3 years then!! lol!!
I have been around I have just had better things to do then spend time on here. I am in a band now that is doing very well and I only found your quote as I was carrying out a google search for something else. I am so glad I do not have work in the electrical/building trade any more. You my be a respected member on here but you a definitely not respected by me.
*********Removed********
Btw to all you other members re the gas pipe, it was a very old 3" in diameter one that was in a 1930's purpose built flat in London. This is why I think the readings were low due to the size of it and parallel paths. Thank you to all of you that responded to me in a helpful manner.
Main earthing by gas pipe.
miLarKey,
Mpe123,