E

egginyourface

went to a job couple of days ago where supplier hadnt supplied earth and looks like it was taking from the water pipe.

Mains water had been up graded to plastic so that wasnt doin the job anymore.

So somewhere down the line someone had come along and stuck a spike in.

I did a test and got a reading of 5ohms. No rcd protection was present. So I told the customer to call energy supplier to come have a look.

To cut a long story short they issued a danger notice and cut the supply at the head by pulling fuse.

Customer calls me with engineer there and tells me theres nothing they can do other than upgrade it to pme but would cost £3,000.

What they offered was that they could strip back sheathing and let me attach earth clamp. they tested the loop impedance from the outer sheathing and they were getting .5ohms.

I refused to use an earth clamp on the sheathing as its illegal for me to mess around with suppliers side of meter.


Is this allowed? Ive seen it many times but never actually put a clamp on the incomer.

Shouldnt it be sweated on by them??
 
This sounds like they must have new rules or just being stubborn. I live in the north west and about two years ago I had the same problem, rewired a house but was getting readings indicating a very poor earth, got onto the local DNO saying the house didnt have a proper earth and they needed them to check their incomer. They came out two days later tested it agreed with me and the stripped the sheath back on went the clamp and put a nice new earth bar on the panel for me and off they went, very simple very good. I would think that if it is a residential area a earth being supplied should be their issue to assume a safe system otherwise we would be knocking ground rods in everywhere! Correct me if am wrong!
 
A TT install is the very last option you would want to go for!! I would be asking at the very top, how they have calculated 3000 quid to PME a domestic installation!! So what earthing system does have all the other houses have in this street?? For a start, I'd be asking neighbours if i could have a quick look at the service heads... If all are PME or TN-S, then there would be some explaining to do as to why they are quoting 3000 quid, for a job that can be done during the service head up-grade at no extra cost to them whatsoever....

If the DNO themselves got a 0.5 ohm, and actually told you to fit your own earthing means to the sheath, then at the end of the day i would be inclined to do just that with the use a constant force spring earthing clamp. No tools required, absolutely no chance of damaging the lead sheath, and a decent earthing point for the installation....

Absolutely amazes me at times here, how fast some will just bung in a twig for an earth rod, be happy with a 200 ohm Ra and walk away ''actually thinking'' they've done a good job!!!
 
talking of constant spring clamps, anyone know where i can buy a set? hand to have,quicker than dno dates and comply with regs,

dno upgrade to pme and shove one on as well as connection to neutral looking at the one the did one my gaff.

didnt pay for it as no earth and old head...
 
Seems the service one receives varies wildly between DNO's. Eon will fit a DP isolator free of charge, plus the guy who did it told me his instructions were to fulfil the customers wishes as much as possible within reason.
I actually felt like I was getting a good service for a change.
 

Reply to main incoming on a tt in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
A bit like saying plumbers makes good electricians. 🥴
Replies
10
Views
1K
Yes the first bit is just standard wiring, TNS lead cable into cut-out, cut-out to meter, meter to DP isolator, top of isolator is sealed as per...
Replies
8
Views
945
  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
833
  • Question
By retired electrician, I mean that I have retained my ticket but no longer do installation work. Thanks for the clarification. I missed that it...
Replies
2
Views
378
  • Question
You need a CT clamp at main tails, it depends on the rules where you are - you used to be allowed wireliss ones (such as MyEnergi Harvi), these...
Replies
14
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks