Are there any circumstances when it might be acceptable to tick the "Continuity and Connection Verified" box of the Electrical Installation Certificate when there is no visual or physical access to the point at which the bonding (normally a clamp in domestic) is applied. If so what checks over and above the requirements for low resistance would be required and are there any references to this in any of the Regs/GNs?
 
i hope you mean EICR, not EIC. because on a EIC, you will have installed the bonding and ensured it is accessible. on a EICR, i would be inclined to enter LIM in the box, with a n ote in the comments section that connection was verified by measurement.

edit: unless you mean a EIC for additional works carried out.
 
i hope you mean EICR, not EIC. because on a EIC, you will have installed the bonding and ensured it is accessible. on a EICR, i would be inclined to enter LIM in the box, with a n ote in the comments section that connection was verified by measurement.

edit: unless you mean a EIC for additional works carried out.
Yes I did mean EIC. I am referring to an addition or alteration where the bonding is already there.
 
yeah, only thought of that after i had pressed the enter button. if the client don't want to pay to upgrade the bonding, then make sure you note on your cert. that it is undersized.
 
ah. just me got confused with t'other thread. note that it's inaccessible but that connection has been verified by resistance measurement to the pipework.
 
Just for your info, the situation you describe is covered on p35 of GN3, "Testing bonding conductors & earthing conductors", As Tel has said, look for low resistance (circa 0.05ohms), between two points e.g. metallic pipes.
 

Reply to Main Protective Conductors - Continuity and Connection Verified - Sighting Clamp in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
303
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
819
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
904

Similar threads

I don't think I'd use it mate even the one line heading then one long paragraph screams ai. And untrustworthy. I don't think much has been edited...
    • Optimistic
Replies
3
Views
932

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top