Last time I used one of my master keys was fault finding on a 660V single phase 2.6MVA supply.
Before that I was paralleling 1.6MVA transformers. I’d only just started with the company and was asked if there was a way of defeating the locked key system! As I said my keys are locked in a chest at home.
Close the Bus Section ACB at the same time another guy has his finger on one of the incomer ACB’s trip.
Shout CLOSED
He shouts OPEN.
If it took 2 seconds we were slow!
Yes it’s dangerous (we were exceeding the maximum fault current 50 KA) but at times needs must, RoB2 will tell you how long it takes to go through a kiln controlled shut down, what took 2 seconds would have resulted in two days down time!
Time to hold my hand up. I’m a rotten barsteward!
I closed the BS after I’d checked the feeder currents.
My mate opened the incomer under near 700A load.
If it had gone wrong, he would have copped the full blast!
I’m a rotten barsteward?
I’ve been next to a 3.3KV 1600A ACB when it opened under fault. I needed new underepants!
Before that I was paralleling 1.6MVA transformers. I’d only just started with the company and was asked if there was a way of defeating the locked key system! As I said my keys are locked in a chest at home.
Close the Bus Section ACB at the same time another guy has his finger on one of the incomer ACB’s trip.
Shout CLOSED
He shouts OPEN.
If it took 2 seconds we were slow!
Yes it’s dangerous (we were exceeding the maximum fault current 50 KA) but at times needs must, RoB2 will tell you how long it takes to go through a kiln controlled shut down, what took 2 seconds would have resulted in two days down time!
Time to hold my hand up. I’m a rotten barsteward!
I closed the BS after I’d checked the feeder currents.
My mate opened the incomer under near 700A load.
If it had gone wrong, he would have copped the full blast!
I’m a rotten barsteward?
I’ve been next to a 3.3KV 1600A ACB when it opened under fault. I needed new underepants!