There is no requirement for RCD protection of socket circuits, unless the installation is considered a special location.
Just wondering whether the meter is single or 3 phase?
 
Good luck with that.
89be3fe547f7827761cd8a9a968ab80a.jpg


4aa244d888ed7955087e3fc4173c1dac.jpg
 
Thanks for that, as you can see from what you have quoted, there is no requirement for the circuit to be provided with RCD protection.

Socket-outlets are required to be provided with RCD protection, not the circuits supplying them, except in some instances where the installation is considered to be a special location, such as Horticultural or Agricultural.
In fact providing RCD protection for such circuits could be a non-compliance in some circumstances.
 
Socket-outlets are required to be provided with RCD protection, not the circuits supplying them, except in some instances where the installation is considered to be a special location, such as Horticultural or Agricultural.
In fact providing RCD protection for such circuits could be a non-compliance in some circumstances.
if the cable is not more than 50mm in wall or has mechanical protection then it needs an rcd
 
if the cable is not more than 50mm in wall or has mechanical protection then it needs an rcd
Still no requirement for socket circuits to be provided with RCD protection.
Yes there are circumstances where it may be advisable, or the simplest solution to provide RCD protection for such a circuit.
However it still remains that there is no requirement in BS7671 for such circuits to be provided with RCD protection, except in some circumstances where the installation is considered to be a special location.
Doesn't matter whether there is a dwelling involved or not.
 
Still no requirement for socket circuits to be provided with RCD protection.
Yes there are circumstances where it may be advisable, or the simplest solution to provide RCD protection for such a circuit.
However it still remains that there is no requirement in BS7671 for such circuits to be provided with RCD protection, except in some circumstances where the installation is considered to be a special location.
Doesn't matter whether there is a dwelling involved or not.

411.3.3

Addition Protection RCD

Socket outlets not exceeding 20 A
 
The difference is the regulations say socket outlet and not circuit. For example you could have the circuit installed surface so doesn't require RCD protection but you would install a RCD socket outlet to comply.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
North

Thread Information

Title
main switch question
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
55

Advert

Thread statistics

Created
paulthemagpie,
Last reply from
paulthemagpie,
Replies
55
Views
4,487

Advert

TrueNAS JBOD Storage Server

Back
Top