No, it came into effect on the 1st Jan 2015 but the 'old' regs don't cease until the 30th June 2015 so the 3rd amendment is actually Currently in effect.
It was published on 1st January, with an effective date of 1st July. So BS 7671:2008 (2013) is still current.
Wrong! this is of the IET website;
Amendment No. 3 to BS 7671 Wiring Regulations will be published on 5 January 2015, and will come into effect on 1 July 2015. The new reference for the book will be ‘BS 7671:2008+A3:2015’.
All new installations must comply with BS 7671:2008+A3:2015 from 1 July 2015.
In this update, a number of potentially life-saving changes have been proposed, which include, but are not limited to, changes to:
consumer unit enclosures (to come into effect January 2016);
wiring in escape routes;
changes to earth fault loop impedances for all protective devices;
the risk assessment approach for the omission of RCDs in non-domestic situations;
updated EIC and EICR forms; and
changes to definitions throughout the Wiring Regulations.
Pleas note, the only place in BS7671 where requirements for circuits to be provided with RCD protection is to be found, is in the section for special locations.
Such circuits are those of a location containing a bath or shower, circuits supplying socket-outlets in Agricultural/Horticultural Installations, etc.
Yes it may well be that the easiest or most cost effective solution will be to provide RCD protection for socket-outlet circuits, rather than individual socket-outlets, but there is no requirement to do so.
It should also be considered that some circumstances, providing RCD protection for socket-outlet circuits can cause nuisance tripping, and could actually be a non-compliance.