Hi, I've changed a consumer unit for a customer but noticed the earth and bonding conductors were undersized at 6mm csa. Do I put this down as a departure from 7671 or not issue to cert until the problem is rectified?

Thanks

Chris
 
Perhaps it would have been best to have tested and replaced if necessary before you changed the CU. that would have been my choice, others may differ though.
 
Hello,

Please do not take this the wrong way, but having looked at your profile you say you are an electrician and not a trainee, so can only give you advise based on this level of standing.

When you carried out all your pre checks and tests on the old consumer unit / fuse box, you would have noticed that the main protective bonding conductors were less that the size they should ideally be.

What size is the main fuse, and what size are the meter tails please.

On the basis the tails are >16mm then I would want to see 10mm bonding conductors to the main services, be it water or gas etc.

Any electrical work that you undertake, the earthing must be up to standard, in my opinion putting it down as a departure on the certificate is not the correct way of doing it as they are there to help save your life, so on that basis, making a note on the cert is not right.

You should have updated the earthing and bonding arrangements prior to your changing the consumer unit or at the same time as, because now, you have energized an installation that is potentially unsafe, ok no worse than it was before, but thats not the point.

Some will say if theres no signs of thermal damage etc to the bonding conductors and the BS951 clamps are in good order with sound connections, but if it was me I would want a 16mm main earthing conductor, and 10mm main protective bonding conductors.

What color is the 6mm you have got, is it green and yellow or solid green?

Also, what size is the earthing conductor and what supply type is it? TNS? TNC-S? TT?
 
With reference to a post you made just 5 days ago, I can only assume this is the same property:

"I would value peoples opinions the earthing arrangement I cam across yesterday. Water and Gas main protective bonding conductors were not installed at the consumer unit, but were coned to the main earthing terminal. The MET was connected to the distributors earth and one conductor ran from the MET to the consumer unit. The resistance from the consumer unit to the gas and water were fine at 0.01 Ohms. But shouldn't the conductors be wired into the consumer unit? They all need changing anyway as they were all 6mm."

http://www.electriciansforums.co.uk...trical-forum/102345-earthing-arrangement.html

So based on this, you knew they were on the small side before you started the work, so why have you carried on and not updated them?
 
Hi, I've changed a consumer unit for a customer but noticed the earth and bonding conductors were undersized at 6mm csa. Do I put this down as a departure from 7671 or not issue to cert until the problem is rectified?

Thanks

Chris

"No addition or alteration, temporary or permanent, shall be made to an existing installation, unless it has been ascertained that the rating and the condition of any existing equipment, including that of the distributor, will be adequate for the altered circumstances. Furthermore, the earthing and bonding arrangements, if necessary for the protective measure applied for the safety of the addition or alteration, shall be adequate."

If you have confirmed that the earthing and bonding arangements are adequate then issue your cert. If not then as you have carried out work then it is up to you to make them adequate.

 
"No addition or alteration, temporary or permanent, shall be made to an existing installation, unless it has been ascertained that the rating and the condition of any existing equipment, including that of the distributor, will be adequate for the altered circumstances. Furthermore, the earthing and bonding arrangements, if necessary for the protective measure applied for the safety of the addition or alteration, shall be adequate."

If you have confirmed that the earthing and bonding arangements are adequate then issue your cert. If not then as you have carried out work then it is up to you to make them adequate.


Hey S, your quote reads as authoritative, please would you quote its source in order to confirm its authority beyond being 'sensible practice' and good advice from an experienced electrician and a moderator or administrator on this site?
 
Hey S, your quote reads as authoritative, please would you quote its source in order to confirm its authority beyond being 'sensible practice' and good advice from an experienced electrician and a moderator or administrator on this site?

I take it you are asking this for the benefit of the OP ? Even though he really should know where this is from being a practising electrician. Not sure it matters anyway as he seems to have cleared off like his last thread.

BS7671, chapter 13 fundamental principles, regulation 132.16 to save Sintra a job.
 
I take it you are asking this for the benefit of the OP ? Even though he really should know where this is from being a practising electrician. Not sure it matters anyway as he seems to have cleared off like his last thread.

BS7671, chapter 13 fundamental principles, regulation 132.16 to save Sintra a job.

A, thanks ... I thought that it was most likely to have been drawn from a recent edition of the BB. I fear that I have been a little lazy, not searching it out for myself. That said ... I was always taught at University to quote my sources!
 
A, thanks ... I thought that it was most likely to have been drawn from a recent edition of the BB. I fear that I have been a little lazy, not searching it out for myself. That said ... I was always taught at University to quote my sources!
I thought you were just being polite with a hint of sarcasm.:smile5:
 

Reply to Major works notification in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
303
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
819
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
897

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top