Got to a customers house today after a brief discussion recently that they have brought a 2kw hob and it needs fittings. I went through the manufacturer’s instructions and they recommend it to be hard wired and that it is to be put on a 32amp breaker, obviously a 2kw appliance will pull around 8amps if my maths is correct so I am wondering am I missing something here? The hard wired part isn’t a problem, it’s more the size of breaker they recommend. There was 2x line and 2x neutral conductors too crimped together (this is where I first thought things weren’t what I am used to)
 

Attachments

  • [ElectriciansForums.net] Manufacturer recommends 32amp breaker for 2kw appliance?
    4D52FC67-207A-4FBE-9E49-0DAC27F13507.jpeg
    390.1 KB · Views: 133
I can relate to the confusion relating to manufacturers instructions.

We took delivery of a new fan oven last week (Smeg). It's under 3000W. Curry's insist that it must be connected to an FCU. Upon unpacking, theres a flex attached without a plug, but also a label on the flex instructing the installer to fit a plug fused at 13A!

The thing is, in our setup, if someone did that along with our new hob, they'd overload the 2 ganger thats there at the moment.

I'm going FCU route anyway, as I reckon it would be hard to argue a correctly fitted FCU is somehow inferior to a plug?
 
Many manufacturers do not rewrite the instruction for the UK market. For example AEG make an integrated fridge that consumes about 1/3 amp. They say it must have a 16A supply. That is totally inappropriate for British ring final circuits. So it must be ignored.

It comes with a 13A plug with a 13A fuse inside for an appliance drawing around 1/3 amp. The cable looks heavy enough to take 16A. The cable looks like it is to be protected by only a 16A MCB at the CU on a radial circuit with a non-fused Euro plug. It look like the 13A fuse does not protect the appliance.

A 3A or 6A fuse will protect this fridge adequately. It does not have to be on 16A supply or a hefty cable in the UK. I assume that it cannot be fitted on a 20A radial as the cable is not man enough to take 20A.
 
Many manufacturers do not rewrite the instruction for the UK market. For example AEG make an integrated fridge that consumes about 1/3 amp. They say it must have a 16A supply. That is totally inappropriate for British ring final circuits. So it must be ignored.

It comes with a 13A plug with a 13A fuse inside for an appliance drawing around 1/3 amp. The cable looks heavy enough to take 16A. The cable looks like it is to be protected by only a 16A MCB at the CU on a radial circuit with a non-fused Euro plug. It look like the 13A fuse does not protect the appliance.

A 3A or 6A fuse will protect this fridge adequately. It does not have to be on 16A supply or a hefty cable in the UK. I assume that it cannot be fitted on a 20A radial as the cable is not man enough to take 20A.
The reason for the larger fuse is the starting surge current.
The fuse is to protect the cable.
 
Last edited:
I'm going FCU route anyway, as I reckon it would be hard to argue a correctly fitted FCU is somehow inferior to a plug?
FCU is better than a plug for sure. But when on for sustained periods the 13A fuse, or connections, can overheat. A small box with a 13A MCB (or 16A - yes you can have a 16A MCB off a ring) and 20A DP switch off the ring would be better for sure. They could be in an adjacent cupboard.

An extreme example.

[ElectriciansForums.net] Manufacturer recommends 32amp breaker for 2kw appliance?


MCB can be in a box like this. About £3-4
[ElectriciansForums.net] Manufacturer recommends 32amp breaker for 2kw appliance?
 
Last edited:

Reply to Manufacturer recommends 32amp breaker for 2kw appliance? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
I’ve been thinking about your cooktop and done the math. Its 7.4kw, so take 7400kw divided by 240vac = 30.8 amps which according to the NEC it...
Replies
7
Views
2K
G
Thanks for your response Richard.
Replies
3
Views
1K
goldie
G

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks