Most DNO's, if asked (by enquiry) would say 16kA is the max PFC available on a single phase 100A or less supply.

I don't for one minute believe the Op's supply is any where near the levels of PFC his meter's are indicating, due to inaccuracies and method of measurement, as many posters here have already pointed out.

Typically EFLI meters measure the volt drop in mV at a measurement of around 20-25A load, and at close to the TX is at the lower end of the instruments capabilities (check the accuracy figures quoted in the user manual).
Under actual kA fault levels it is doubtful the TX could even supply the installation at that level of fault current before the cut fuse failed

The OP would either need a more accurate meter, or use IQ's method of measurement, as any slight discrepancy in the loop reading has a massive bearing on the PFC reading.

When you consider the DNO's supply cable has some resistance, as well as the cut out fuse and the meter itself as well the tails, then the calculations don't really add up, as the fuse, the Dno's cable, the meter and the tails would need a total resistance of 0.001 ohms for a PFC of 23kA single phase calculated @ 230V
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Southend on sea ESSEX

Thread Information

Title
Max PFC gone through the roof....Ideas anyone?
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
46

Thread Tags

Advert

Thread statistics

Created
Eggster71,
Last reply from
spark 68,
Replies
46
Views
6,167

Advert

Back
Top