max volt drop to sub board 3 core swa 137 meters ?
25mm2 swa on a b50 breaker 1.75 times 50 times 137 _ 11.9v still overIs that a question or a suggestion?
Sorry Mate not making sense. you mention 10mm2 what was that all about?25mm2 swa on a b50 breaker 1.75 times 50 times 137 _ 11.9v still over
what would you guys do if you where doing the job rather just be told thanks tho i do appreciate you guys helping me and no iam not just ignoring the volt drop sorry i ment to reply to you mate
The requirement according to BS7671 is 3%. The type of installed fittings is not relevant.