Hi I have a 15th edition of the regs which gives disconnection times - The question I think is why are these times not in the 17th edition ?? even as a suplument ?? I have always used the ratings from the 15th edition of the regs ??
 
Hi I have a 15th edition of the regs which gives disconnection times - The question I think is why are these times not in the 17th edition ?? even as a suplument ?? I have always used the ratings from the 15th edition of the regs ??


No you can not use the 15th or 16th values as these are based on the voltage being 240v and not 230v as is now used under harmonisation.
 
There is a table on the inside page of the NICEIC certificates stating all the max Zs ratings for 3871's 88's 1361's 1362's and 3036's.
 
just googled this to check and

17th Edition Maximum Ze & Zs Values

states "BS7671 does not give maximum Zs values for BS 3871 mcb's"

If you have the disconnection time, device manufacturer (if not i can use generic) and rating I can use my software (single cable) to find the values.

Hi guys, James here with first post!


Does anyone know the max permitted Zs for a 32A type 4 3871 mcb?

Many thanks to anyone who can help, cheers


James.


5s = 1.0034
0.4s = 0.5134

Taken from Single Cable 17th eddition generic values
 
Last edited by a moderator:

Reply to Max ZS for BS 3871's in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
434
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
935
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
892

Similar threads

I created a voltage drop spreadsheet for this sort of thing. I used to use it to calculate the drop when designing regular 230V lighting circuits...
Replies
24
Views
1K
If the shared neutral is lost ,won`t you be getting 400v across both cottages? 2 phase US style but double the Voltage.
Replies
22
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top