I have noticed, a lot of max Zs readings on test certs (Where RCD's are applicable) are being blanket recorded at 1667 ohms.
On a personnel note I consider this to be poor practice, and prefer to see max Z's taken from tables 41.2 41.3 and 41.4 of chapter 41 of the good old guide.
My reasons are that 1667 is an unrealistic figure in most cases. and doesn't promote a true solid reliable earth fault return path (Like in the good old days before RCD reliance)
We all know that RCD's offer suplementary shock protection, and thats fair enough but chucking 1667 around like conffetti detracts from what a proper earth fault path is really all about.
Maybe I'm getting padantic in my old age, but its one of those things that bug me.
And if an RCD fails its nice to know the earth fault path will be low enough to take out the overcurrent device before touch voltages rise to a point that Zap's people.
RCD or no RCD. (TT aside that is)
(Rant over)
On a personnel note I consider this to be poor practice, and prefer to see max Z's taken from tables 41.2 41.3 and 41.4 of chapter 41 of the good old guide.
My reasons are that 1667 is an unrealistic figure in most cases. and doesn't promote a true solid reliable earth fault return path (Like in the good old days before RCD reliance)
We all know that RCD's offer suplementary shock protection, and thats fair enough but chucking 1667 around like conffetti detracts from what a proper earth fault path is really all about.
Maybe I'm getting padantic in my old age, but its one of those things that bug me.
And if an RCD fails its nice to know the earth fault path will be low enough to take out the overcurrent device before touch voltages rise to a point that Zap's people.
RCD or no RCD. (TT aside that is)
(Rant over)